It's like glanding an SWA onto galvanised trunking, you wouldn't fit a banjo then would you?

It depends, If I am using the SWA as the earth or I cant banjo it the other end of the cable for some reason then I will banjo it to the galv trunking.
I have always been of the opinion that even if you dont technically need it if it is there why not fit it?
Unless of course it means running in 20m of earth single or it would look stupid or out of place but thats a different kettle of fish.
 
It depends, If I am using the SWA as the earth or I cant banjo it the other end of the cable for some reason then I will banjo it to the galv trunking.
I have always been of the opinion that even if you dont technically need it if it is there why not fit it?
Unless of course it means running in 20m of earth single or it would look stupid or out of place but thats a different kettle of fish.

I don't get it, if you drill teh hole the right size and tighten the locknut properly then that makes a good metal to metal connection so why the banjo?
And what do you do with the banjo, just stick a bolt through it to hold it to the trunking?
 
Nope, I put a bolt through with a crimped wire attached and run to the nearest earth point.
Doesn't everyone?? :s

The purpose being to ensure it is earthed correctly.
After all you are assuming that the trunking is correctly earthed, which from my experience its not!
 
But the trunking is your CPC, why on earth would it not be earthed?

Why would you install a seperate earth wire inside the trunking which has a csa a few orders of magnitude bigger?
 
I was always taught its good practice.

Just to play devils advocate if you were to install a armoured into a galv trunking do you go and check that every screw and bond is in place? Can you guarantee that nobody has come along and modified it, removed a link? Hell I have seen a few that were not bonded at all!

Like I said for the sake of drilling a 6mm hole (which is the size of a pilot drill for most hole saws) and putting a bolt and crimp on whats the harm?

I agree they are not really needed normally but I can say its there.
Ime sure there used to be a reg that said a SWA had to be banjo's at least one side anyway?
 
If it is existing trunking and it is not in acceptable condition then I would not be glanding an SWA onto it my installation would not be compliant.
Steel trunking must be effectively earthed in its entirety, if it is not then it does not comply.
 
Ok I will give you a prime example,

I did some work in a office, The desks had a 2x4 Metal powder coated galv compartment trunking drop to each row going under them, They were fed from a SWA fed from a board half way down the office.

So I linked out each section with a link. So where was I meant to earth it?
I could rely on just the 6mm crimped lugs screwed to each section of the trunking and wired into a socket, But I would rather Banjo the gland as well just to be on the safe side.

At the end of the day I would rather put that extra earth path in as its a doddle to do and doesnt take me any more significant time.
If you dont want to I wont hold it against you :p
 
Powder coated trunking is a little different, I would be looking at an additional connection to the gland, the same as with a painted surface.
I would use an earth nut or a CMP ciel type gland for preference over a banjo.

My earlier comments have all been about bare metal, apologies if that was not clear.

To be honest I prefer to screw the gland in to a flange coupler and attach that to the trunking with a serrated washer than just attaching the gland straight to the trunking anyways.
 
Yeah new ones are pretty crap.
I found a stash of old ones the other day in a drawer though so I have been using them the last few weeks.
You can even get a spanner on em!!
Why dont they make em like they used to :(
 
Got to say an earth tag does have a greater contact area than a gland /l.nut, the larger size tags 50-63-75 are rated at 10.40ka fault current so when the cables armour can exceed that value and there is a possibility that it might have to a gland with an integral earth boss should be used ,so the idea that the gland / termination doesn,t need earthing and that the trunking / gland plate is acceptable needs to be checked out.Can,t find the ka rating of glands though.
 
Got to say an earth tag does have a greater contact area than a gland /l.nut, the larger size tags 50-63-75 are rated at 10.40ka fault current so when the cables armour can exceed that value and there is a possibility that it might have to a gland with an integral earth boss should be used ,so the idea that the gland / termination doesn,t need earthing and that the trunking / gland plate is acceptable needs to be checked out.Can,t find the ka rating of glands though.

So where is that going to help when the fault level at the transformer is liable to be around 25KA?
 
Just cable installations in general, it would be wrong to assume that a piece of trunking or gland plate on its own is ok to gland into without checking possible fault currents
 
Think the argument is 50/50 about the clamping the cables down although it gives that professional finish but must agree with everyone else ... heat shrink a must - tape is rough and you rely on the tape gum for the life span of the equipment although it poses not real safety risk a few yrs down the line your tape could be pealing and giving your work a poor reputation to anyone that follows you. Having said that if all your been pulled for is lack of heat shrink and a debatable lack of fixing then I wouldn't fret too much and take the advice on board.


Just spotted this post DW.

The jury has returned with a verdict. Have a look elsewhere for a topic on transformer tails. In particular the bit about magnetic reaction under fault conditions. It’s not a case of they look better, it’s a matter of safety.
 
One poor sod got chopped in half by trench cover plates being thrown in the air.

That was back in the 80’s, a couple of months before I started re-cabling a substation. For some strange reason we had a bit of a rethink about the job. I’ve had a bee in my bonnet ever since.

OK you can use the reasoning, what are the chances of it happening?
Quite high, the substation above one of the mates let a ¼” chequer plate drop in to the trench. There was 28x500mm cleated to the sides, fortunately it only skinned the outer serving off a few of them. Had it gone through the insulation there would have been 4x1000KVA 11/.433KV transformers feeding the fault.

Can’t say I was too happy, I had to repair the cables. A week after we’d put them in.
 
Tony, in the op pictures, do you think that not cleating the spaced cable vertical drops could be dangerous under fault conditions in this situation? The reason I ask is because they are't run in trifoils but are rather entering up vertically spaced apart?
 
The distance between them is about the only saving grace.

Depending on how they are fastened in the trench has a bearing on the drops from the terminal box. If they can move in the trench then damage will be done to the terminals.

I would put them in single cleats anyway.
 
Well I knew big cables were rated for big fault current but I never realised they could react like that!!
Though yes It would make many things seem pointless and insignificant.
Its funny I have been in a few subs and allways given the stuff a wide birth when I didnt have to be near it but think ile have to stay clear of the ladder racks to now LOL
 

Reply to Sexual - Still makes me tingle in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi Guys I seem to have an issue with voltage coming back from a QTX 15 pa I was getting a lot of hum (I have a pair and confirmed it's the same on...
Replies
2
Views
190
I haven't received part of my order from superlec. Its been 3 months. Lots of phone calls, lots of promises, nothing happens. Just wondering if...
Replies
9
Views
699
On the Napit certification page there is a little tick box, saying something along the lines of ' I consent to this job being used for my...
Replies
19
Views
1K
Facts: Thinkbook 14 G4 AIP - laptop A Thinkbook 14G4 AIP supplied power adaptor - adaptor A (65w usb-c, fake plastic ground for UK socket) is...
Replies
1
Views
747
I would like to reuse a 10mm cable to provide a ring circuit in an area. The cable is currently used for an electric shower, still connected at...
Replies
10
Views
436

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock