Got to say an earth tag does have a greater contact area than a gland /l.nut, the larger size tags 50-63-75 are rated at 10.40ka fault current so when the cables armour can exceed that value and there is a possibility that it might have to a gland with an integral earth boss should be used ,so the idea that the gland / termination doesn,t need earthing and that the trunking / gland plate is acceptable needs to be checked out.Can,t find the ka rating of glands though.
 
Got to say an earth tag does have a greater contact area than a gland /l.nut, the larger size tags 50-63-75 are rated at 10.40ka fault current so when the cables armour can exceed that value and there is a possibility that it might have to a gland with an integral earth boss should be used ,so the idea that the gland / termination doesn,t need earthing and that the trunking / gland plate is acceptable needs to be checked out.Can,t find the ka rating of glands though.

So where is that going to help when the fault level at the transformer is liable to be around 25KA?
 
Think the argument is 50/50 about the clamping the cables down although it gives that professional finish but must agree with everyone else ... heat shrink a must - tape is rough and you rely on the tape gum for the life span of the equipment although it poses not real safety risk a few yrs down the line your tape could be pealing and giving your work a poor reputation to anyone that follows you. Having said that if all your been pulled for is lack of heat shrink and a debatable lack of fixing then I wouldn't fret too much and take the advice on board.


Just spotted this post DW.

The jury has returned with a verdict. Have a look elsewhere for a topic on transformer tails. In particular the bit about magnetic reaction under fault conditions. It’s not a case of they look better, it’s a matter of safety.
 
Just spotted this post DW.

The jury has returned with a verdict. Have a look elsewhere for a topic on transformer tails. In particular the bit about magnetic reaction under fault conditions. It’s not a case of they look better, it’s a matter of safety.

Cleated cables on ladder under fault conditions:
https://www.youtube.com/watch?v=YZiTmk7cDrM
 
One poor sod got chopped in half by trench cover plates being thrown in the air.

That was back in the 80’s, a couple of months before I started re-cabling a substation. For some strange reason we had a bit of a rethink about the job. I’ve had a bee in my bonnet ever since.

OK you can use the reasoning, what are the chances of it happening?
Quite high, the substation above one of the mates let a ¼” chequer plate drop in to the trench. There was 28x500mm cleated to the sides, fortunately it only skinned the outer serving off a few of them. Had it gone through the insulation there would have been 4x1000KVA 11/.433KV transformers feeding the fault.

Can’t say I was too happy, I had to repair the cables. A week after we’d put them in.
 
Tony, in the op pictures, do you think that not cleating the spaced cable vertical drops could be dangerous under fault conditions in this situation? The reason I ask is because they are't run in trifoils but are rather entering up vertically spaced apart?
 
The distance between them is about the only saving grace.

Depending on how they are fastened in the trench has a bearing on the drops from the terminal box. If they can move in the trench then damage will be done to the terminals.

I would put them in single cleats anyway.
 
Well I knew big cables were rated for big fault current but I never realised they could react like that!!
Though yes It would make many things seem pointless and insignificant.
Its funny I have been in a few subs and allways given the stuff a wide birth when I didnt have to be near it but think ile have to stay clear of the ladder racks to now LOL
 

Reply to Sexual - Still makes me tingle in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock