We have been doing work in a flat where we had taken down light and put a temp ceiling rose. All was fine for a month then we fitted new expensive chandeliers. Worked fine for a few weeks then on some mornings the circuit would trip with a bang. Went back did a ir test all was clear 10m ohms between n-e l-e. Tested light that it was blowing from all was clear. Left off for a few days no problem. Refitted it and after a week it starts happening again. Light supplier says it carnt be the light as it would not cause a short. Any thoughts it run in singles in conduit.
 
N-E OK, L-E OK what is left?
You have a short occurring between Line and Neutral!
Since they are chandeliers are they class II if so then you can restrict fault finding to the light switch and the ceiling connections as the most liekly culprits.
If you have had numerous shorts then the smoke damage and melted copper should be obvious.
 
Yes but there are alot of lights a a few fans on the circuuit so did not want to damage them. Would it not happen all the time if there was a wire fault. Some time a week passes no problems. How likley is a l-n fault
 
Yes but there are alot of lights a a few fans on the circuuit so did not want to damage them. Would it not happen all the time if there was a wire fault. Some time a week passes no problems. How likley is a l-n fault

Fans!!!!!! Do you even know it's your light fitting that is causing the tripping?
 
Light supplier says it carnt be the light as it would not cause a short

Huh? I suppose it's made by the same people who do the unsinkable ships and future-proof computers. Or do they just have a fancy name for when the brown and blue wires touch together?
 
Yes i am. Why all the negativity- just asking if anyone hada idea how could it only happen occasionally and what other way is there to find it then? The light are class 1 iv never come across a fault like this. As said when light was removed nothing blew. There was another light on the same switch which we left on with no problems
 
How do you know your light is responsible?? You said previously there were fans on thesame circuit?
 
iv never come across a fault like this

You have been living a privileged life. I certainly knew what to expect of intermittent faults and how to search for them by the time I was 8 or so. Tricky ones can make your life hell. OTOH this is a light fitting so it's not going to be very tricky, although you might have to rip it apart to prove beyond all doubt.
 
Yes but there are alot of lights a a few fans on the circuuit so did not want to damage them. Would it not happen all the time if there was a wire fault. Some time a week passes no problems. How likley is a l-n fault
Do the fans have isolation switches?
You won't be sticking any voltage through them if you isolate them.

If not, as previously said, you're pulling it to bits to test I think.
 
OK think about what is happening just for a moment.
We do not know the situation and arrangement, however, suppose everything is OK when the new light is not in place, (although you have said it can be OK for a week or more so not a definite).
This narrows the fault down to the light fitting itself, not the fans (which I might suspect) or the light switches or the circuit wiring.
The fault is tripping an MCB (if there is an RCD on the circuit and it is not tripping that then the line neutral fault is confirmed, without an RCD it could still be an intermittent Line Earth fault).
Therefore there is a short occurring intermittently.
Can the chandelier move in a wind or such like, does it get shaken by someone walking over the floor above it?
Have you checked all the wiring in the fitting to see if there is a loose wire, a faulty bulb, a bare wire in the ceiling just touching a metal hook, etc. have you looked for signs of a short circuit, black around a wire or part,etc.?
Did you IR test at the fitting?

Why am I typing this, I need to go to sleep!
 
I have identified which light it is. There are two lighys on one switch. Its not the fans i no as it only happens with this one switch when turned on. Once the fault occurs they reset it and all works as it should. No the chandelier can not move concrete ceiling the light takes small screw which have been going on most of the lights quite quickly its on a rcbo but as said when tested l-e n-e all clean from light switch and db. I tested the light itself and was all clear with no bulbs. If there was a fault between l-n would it not of happened with light not connected as other light was still on causing power to flow.
 