Hi all
Question regarding shower circuit designs. How so many times I see 6mm t&e cables supplying shower circuits on a 40amp MCB ? So for example if you were carrying out a EICR and you noticed a 6mm t&e cable on a 40amp MCB, 8.5kw/9kw shower would you put this down as a C3 or would you not put anything at all ? Giving that you don’t know how the cable is installed ? I have came across a few that when inspecting the cable has came from consumer unit up through floor floor boards and up inside external wall/pipe duct. Run approx 18 to 20meters. Now with not knowing the installation method if tangled in insulation in wall or bunched under the floor boards. Going with current carrying capacity 6mm good for 47amps but add in the factors could bring this down. Do you quote customer for changing MCB or do you make note of it on test sheet, or just leave as is ? Would like to hear other opinions ??
Question regarding shower circuit designs. How so many times I see 6mm t&e cables supplying shower circuits on a 40amp MCB ? So for example if you were carrying out a EICR and you noticed a 6mm t&e cable on a 40amp MCB, 8.5kw/9kw shower would you put this down as a C3 or would you not put anything at all ? Giving that you don’t know how the cable is installed ? I have came across a few that when inspecting the cable has came from consumer unit up through floor floor boards and up inside external wall/pipe duct. Run approx 18 to 20meters. Now with not knowing the installation method if tangled in insulation in wall or bunched under the floor boards. Going with current carrying capacity 6mm good for 47amps but add in the factors could bring this down. Do you quote customer for changing MCB or do you make note of it on test sheet, or just leave as is ? Would like to hear other opinions ??