I am dealing with a similar case just now. A house I own and rent out was due for its 5 year EICR. While doing the EICR I asked the tenant if there was any problems with the installation, just the shower they said, if two people have a shower one after the other or the daughter is in it for a while it trips out. Turns out the tenant had up graded the shower without my knowledge to a 8kW on a 6mm cable with 32A MCB. I know the cable is clipped in the floor void then up inside an uninsulated lath and plaster wall and there is no sign of any distress at the connections so I am going to change the 32AMCB to a 40A RCBO once the current madness is over.