so what about cables in the voids between floors.? surely these aren't B. i'd class then as in free air, unless clipped to joists, i.e C.
According to Table 4A2 Method C applies to cables fitted direct to walls and ceilings, in masonry walls and cables on unperforated trays. Strictly speaking according to this Table cables in floor voids would be Method B.
 
I am dealing with a similar case just now. A house I own and rent out was due for its 5 year EICR. While doing the EICR I asked the tenant if there was any problems with the installation, just the shower they said, if two people have a shower one after the other or the daughter is in it for a while it trips out. Turns out the tenant had up graded the shower without my knowledge to a 8kW on a 6mm cable with 32A MCB. I know the cable is clipped in the floor void then up inside an uninsulated lath and plaster wall and there is no sign of any distress at the connections so I am going to change the 32AMCB to a 40A RCBO once the current madness is over.
 
Yeah looking at table 4D5 it should be reference method C clipped direct. As the cable is not in 100mm insulation in wall. I think that will be best option remove any insulation around the cable in attic away and check electrical connections for any damaged insulation/over heating etc. That way don’t have to change 40amp to 32amp In Case of potential constant overload and I have made the current rating of the cable better with clipped direct and check that there is no signs of over heating ? This like said will get done when current climate get back to normal
 