tuckermot

Hi
would you still have a fused:) spur (3 A ) as well as a 3pole isolator for a shower fan with timer .The fan is a in line in the loft ( supply from light fitting)

thanxs
Rich
 
Last edited by a moderator:
Hi
would you still have a fused:) spur (3 A ) as well as a 3pole isolator for a shower fan with timer .The fan is a in line in the loft ( supply from light fitting)

thanxs
Rich

Instead of a 3-pole isolator,fit a switched fused spur for the supply
You then have double pole isolation and a 3-amp fuse
 