How often will it be used? Is a silenced diesel generator with remote start an option? Probably £85k cheaper than what the DNO have quoted and possibly cheaper ongoing.
It is correct that a lift for general use could be incorporated into an escape plan in an emergency situation after a risk assessment and a controlled strategic plan but generally this would be considered a high risk policy. Lifts which have been put in place as part of an escape route are subject to strict legal requirements and are generally only considered where vertical footfall is not free flowing such as a hospital where mobility may be restricted.
The motor is rated at under 12kW.
You can use a 1ph - 3ph VFD to control just a 3ph motor. The existing controls would be wired to the VFD controls, fairly simple if you understand the way the lift works and safety requirements etc.
But will the lift company want/know how to redesign their lift for a one off project?
No.