Afternoon all

This is based on a previous thread I’ve worked on, carried out an assessment on site , found a imperial aluminium sheathed copper single supply cables measuring at 10mm diameter on the strands themselves , what size of cable does this make it? And what is the copper equivalent now?

Thanks in advance !
 
Is the the same conductor as in your previous pics.
 
Have you established if it is aluminium or tinned copper.
 
10.6mm dia = 25mm2 or 4 AWG
 
That makes it approx 78mm sq.
 
(10×10)×(pi÷4).
 
(10×10)×(pi÷4).
I'm agreeing with you, just annoyed at myself that rather than doing it manually I referenced Google instead, and the first up result was wrong and I didn't double check!
 
  • Like
Reactions: westward10
10mm dia.= 5mm radius, so csa = 5 sq. x pi. as westie's post.
 
aluminium sheathed copper single

We now have three chat threads about one cable and it's been called aluminium, tinned copper and now aluminium sheathed copper whatever that might be. I think we can see that clearly in the pics it's not sheathed, it's a single-insulated tinned copper stranded single-core conduit cable. Just a bog-standard conduit cable like every other conduit cable of its age, albeit quite a large one. Please can we stick to that description unless proven wrong and keep it all together in one thread?

10mm diameter would give 79mm² if it were solid, but it is stranded so there is some air space within that diameter. It is quite likely to be 0.1 sq. ins. (65mm²) of 19/.083 construction which is what I was leaning towards having seen the second set of pics. A 19-strand conductor has an overall diameter of about five times the diameter of one strand (draw it!) and 0.083 in = 2.1mm, so this checks out reasonably well. Obviously the best method to confirm is to measure one strand with a micrometer.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Size of imperial cable
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
15

Advert

Thread statistics

Created
Storm93,
Last reply from
Lucien Nunes,
Replies
15
Views
3,105

Advert