Hi Everyone

May be someone could shed some insight on the sizing and provide some suggestions:

3 phase Generators (400 V, 50 Hz) have the ability to sustain 250% kVA of its rated kVA at 30% voltage dip.

Suppose a machine needs to be powered by a standby generator during a power outage. It has 3 Nos. motors that start simultaneously as follows:
1 No. 11 kW (Start via VFD)
1 No. 2.5 kW (D.O.L)
1 No. 2.5 kW(D.O.L)

The Diversity Factor is 1


The Start kVA (11 kW motor) = 1.6 x (kW/ starting P.F) = 1.6 x (11/0.8) = 22

The Start kVA (2.5 kW motor) = 8 x (kW/ starting P.F) = 8 x (2.5/0.7) = 29 kVA

The Start kVA (2.5 kW motor) = 8 x (kW/ starting P.F) = 8 x (2.5/0.7) = 29 kVA

Total Starting kVA = 22 + 29 +29 = 80 kVA & Running kVA about 22 kVA (including lighting)

1. Since the Generator can sustain 250% of its rated kVA for 10 seconds, can a 50 kVA Generator rating be selected as all the motors will be started in less than 10 secs.

2. Someone who is used with generator sizing maybe could provide the multiplying factors for VFD, soft starter, DOL, and Star-delta, and a good insight of generator sizing for the above.

Regards
 
Before investing in a unit that big that will cost a lot of money, I would hire a 22kw unit ant try it out.

My gut feeling says it will be enough, the fuel usage of a 22kw is a lot less than a 59kw unit when running less than 16kw of load.
 
Certainly worth looking at the cost (initial and running) as it might work out cheaper if you have problems to install soft-start units than to over-size the generator.
[automerge]1592119335[/automerge]
Running diesel engines at small fractional load is not good for them either so that is another thing to consider (look up "wet stacking") but maybe not a big issue at ~1/4 load.
 
Is this real life or theoretical / training?
Are the motors starting on full load or no load?

A generator is only as good as the engine driving it, one generator may have and engine with 50% more power compared to another, both with the same KVA rated generator.
You wouldn't want to rely on driving the generator at + 250% every time it starts up.

I can't help with the calculated sizing but can tell you that the 2 x 2.5 kw motors will be up to full speed before the 11kw Vsd controlled motor is hardly moving /taking current.

As above re pc1966 running at fractional load, but same also applies to running at near full rated load is not good for fuel useage either.
 
Is this real life or theoretical / training?
Are the motors starting on full load or no load?

A generator is only as good as the engine driving it, one generator may have and engine with 50% more power compared to another, both with the same KVA rated generator.
You wouldn't want to rely on driving the generator at + 250% every time it starts up.

I can't help with the calculated sizing but can tell you that the 2 x 2.5 kw motors will be up to full speed before the 11kw Vsd controlled motor is hardly moving /taking current.

As above re pc1966 running at fractional load, but same also applies to run at near full rated load is not good for fuel usage either.
Its a real application and all the motor starts on the fly and on load.
Good point - the smaller motors will reach full speed well before the VSD controller motor.
 

Reply to Sizing 3 phase Generator in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a 230 Volt single-phase circuit with a 100 Amp cutout fuse and a 100 Amp MCB switch, so the supply is rated at 23 kVA. Only about 13% of...
Replies
54
Views
6K
Iv been asked to wire a separator (portable to go to different farms and separate water from slurry) to a 3phase 40 kva generator. The separator...
Replies
4
Views
2K
wiring a 480 volt 3 phase 114 amp generator to run 2 machines. Both machine nameplate 480 v 3 phase 50 FLA. What size wire and over current...
Replies
0
Views
941
Hello, I am hoping this is in the correct forum. To start, I acquired a film processing machine that runs on 3 phase. Now before getting the...
Replies
19
Views
3K
Posted this to the DIY section since I'm not a business or employee in this matter but it feels more appropriate (and might actually get...
Replies
0
Views
775

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock