NPower have arranged a date to replace the isolator free of charge.
I note the comments about the fuse protecting the cable. Is this required by the regulations?
The SWA leaves the meter box at the bottom and then runs up the outside wall to the ceiling level (it is a bungalow) and through the loft to the consumer unit located in the hall cupboard in the centre of the property. This distance is well over 3 metres, probably nearer 10-15 metres. The meter box probably dates to 1981 when the property was built. The isolator was probably fitted when an extension was added about 6-7 years ago and the consumer unit fitted.
They won't replace that isolator, it doesn't belong to them it belongs to you. I think they have assumed they have an existing isolator they supplied to replace.
The fused isolator is required by the wiring regs to protect the distribution cable and the fuse should not be taken out of the equation. It could possibly be changed for a smaller unit but this would need to be done by an electrician not your energy supplier.
What you don't want to is for a clueless meter fitter to remove the fused unit and replace it with one of their unfused units so they can wedge a smart meter in.
Why do you want a smart meter ? Your current meter still works well enough right ?