I have asked E.org what the mobile phone signal strength is when they installed the 1st and 2nd SM. The house is in a poor signal area. Would the need to boost the signal from the SM cause interference in the CU?
Will get tenant to take pic when next trip.
 
This is a situation crying out for more in-depth testing,including data logging,etc.
I hold minimal faith,in BG being capable of delivering this...
4 electrical checks - 3 by BG, last one by PH Jones.
What exactly regarding in depth checks are needed, so I can request these be made.
I feel responsible for tenant, as not fair they are living with RCD tripping constantly, and who knows how long Energy Ombudsman get to resolution, 8 weeks, after xmas!
 
As far as I know, mobile modems vary their signal strength based on the strength of the signal they receive, so if the signal is weak, they'll increase their output accordingly.
Yup, the weaker the signal the more power the send out trying to get good comms with the local mast.
 
Even if there is a neutral-earth fault downstream, there would still be no leak as long as there is no potential difference between earth and neutral.

If there was a neutral earth fault downstream e.g. shorted together then there would indeed be no PD but there would be earth leakage, it will parrallel the neutral return current through the cpc. If RCD protected then that would trip from the L-N inbalance
 
4 electrical checks - 3 by BG, last one by PH Jones.
What exactly regarding in depth checks are needed, so I can request these be made.
I feel responsible for tenant, as not fair they are living with RCD tripping constantly, and who knows how long Energy Ombudsman get to resolution, 8 weeks, after xmas!

To be fair, I think the BG spark has done what he can. He has taken Zs to prove effective connection to earth. He has taken IR at 250vdc. He likely selected 250vdc so he could test with loads connected to eliminate both wiring and loads for earth faults. Sensible. He has also ramp tested RCD.

I agree with others that it may well be interference from meter comms mobile being so close to RCD. IIRC the RCD in that board will be an MEM with a functional earth wire it may act like an antennae!
 
Last edited:
Hi - From afar I guess we can never solve this, but there are couple more things for an Electrician to look at in my view. Did the BG Electrician actually personally observe the remote test and the tripping RCD? I would be seeking cooperation from the meter company with some more testing. Something like : Standing at the box with main switch, RCD and all circuits on, have the remote test done and observe the RCD trip. Reset RCD and turn all MCBs off and repeat the remote test and observe any trip. Safely remove the outgoing N from the RCD (still leaving all MCBs off) and repeat the remote test and observe any trip.
 
I remember a thread on here a few years ago where on a site walkie talkies were the cause of RCBO’s tripping. And I think it was the same thread where @GMES had the same or knew someone who had the same issue with over 300 RCD sockets and walkie talkies.
 
You need to find someone with an electromagnetic radiation tester to see what the meter output is.
 