Thought I would throw my tenant's problem regards Smart Meters (SM) into the mix, in the hope someone could maybe suggest what is going on?

May 2016 - tenants switch to E.org - no problem.
March 2017 - had Liberty 100 PAYG SM (top-Up via App) installed and immediately the RCD/fusebox starts tripping intermittently - every few hours, every day, after few days - see picture.
April 2017 - I contacted E.org and they stated that SM not cause switches to trip, fault is fusebox. Accept what they say.

Tripping continues and tenants check and monitor if appliances causing problem. None found.
BG electricians check home electrics 4 times and state domestic side and RCD all ok - Dec 2017, Aug 2018, Sept 2018 and Oct 2018.

After much elimination find Cause???!!!
Customer Top Up - when tenant tops up via app and then a few minutes later credit shows up on phone, then RCD immediately trips.
Supplier reading - after informing E.org about above and they do On Demand reading from their end, then RCD immediately trips.

E.org change SM Oct 2018 and tripping now worse.
BG check after SM change and state domestic side and RCD all ok.
E.org state that fault is RCD as have changed SM and thus are insistent they are not at fault.
BG believe it is SM, so I am between a rock and hard place.
Requested E.org replace SM with Dumb Meters as a way of eliminating or confirming SM is cause of tripping, but will only do if I pay.

Now starting case with Energy Ombudsman… And tenants’ life not good as now 3/4 times a day have to reset RCD.
Any ideas/advice?

Liberty 100 SM next to RCD.jpeg
 
Aico Carbon Monoxide Detectors
This official sponsor may provide discounts for members
O

Octopus

Get a local independent spark through recommendation to check it out

It’s hard to believe that topping up a meter can trip a rcd

Have you got a picture with the fuseboard cover open so we can see the breakers?
 
D

Deleted member 26818

Theoretically, there should be reason that the meter can cause a downstream RCD to trip.
 

Marvo

-
Mentor
Arms
Esteemed
Probably not the kind of advice I should be posting on the publicly viewable forum but I'd either relocate the meter a greater distance from the CU or I'd wrap the CU in thick tin foil with a bonding wire attached to it and see if the nuisance tripping stops. Obviously isolate, and do a risk assessment first etc.

Smart meters can have fairly powerful WAN transmitters and even GSM transmitters which could cause issues with RCD's if in very close proximity.
 
the only way to cause an imbalance on a downstream RCD is to cause a leak from one of its outgoing live conductors. Even if there is a neutral-earth fault downstream, there would still be no leak as long as there is no potential difference between earth and neutral.
If the smart meter could cause a change the potential on the neutral above earth, it would cause an imbalance in the presence of a N-E fault.
Has someone actually IR tested the neutral bar with main switch off to the MET with the main earth and all bonding and cpcs connected?
 
O

Octopus

the only way to cause an imbalance on a downstream RCD is to cause a leak from one of its outgoing live conductors. Even if there is a neutral-earth fault downstream, there would still be no leak as long as there is no potential difference between earth and neutral.
If the smart meter could cause a change the potential on the neutral above earth, it would cause an imbalance in the presence of a N-E fault.
Has someone actually IR tested the neutral bar with main switch off to the MET with the main earth and all bonding and cpcs connected?
I’ve given you a disagree because lose connections on the supply side can and do trip rcds
 
  • Thread Starter Thread Starter
  • #12
Will request tenant send me pic with fuseboard cover open. And reason taken so long from initial problem starting immediately when change to SM in March 2017 and going to Energy Ombudsman now is that we also could not believe top up cause RCD trip - but it is true! Also, please see below BG report picture from 11 Oct 2018.

elecforum BGReport.jpg
 
I’ve given you a disagree because lose connections on the supply side can and do trip rcds
Agree completely, that's why I said "cause an imbalance" because I know there are other ways to trip an RCD.
I just wanted to get the obvious question about whether it was tested properly out of the way!
Given the BG guy has written "power trips out" which is useless without saying what trips (presumably the RCD), I wouldn't be sure they had an eye for precision.
 

PEG

-
Mentor
Arms
Esteemed
This is a situation crying out for more in-depth testing,including data logging,etc.
I hold minimal faith,in BG being capable of delivering this...
 
  • Thread Starter Thread Starter
  • #20
I have asked E.org what the mobile phone signal strength is when they installed the 1st and 2nd SM. The house is in a poor signal area. Would the need to boost the signal from the SM cause interference in the CU?
Will get tenant to take pic when next trip.
 

SparkyChick

Mod
Mentor
Arms
Esteemed
As far as I know, mobile modems vary their signal strength based on the strength of the signal they receive, so if the signal is weak, they'll increase their output accordingly.
 
  • Thread Starter Thread Starter
  • #23
This is a situation crying out for more in-depth testing,including data logging,etc.
I hold minimal faith,in BG being capable of delivering this...
4 electrical checks - 3 by BG, last one by PH Jones.
What exactly regarding in depth checks are needed, so I can request these be made.
I feel responsible for tenant, as not fair they are living with RCD tripping constantly, and who knows how long Energy Ombudsman get to resolution, 8 weeks, after xmas!
 

Strima

-
Arms
Esteemed
As far as I know, mobile modems vary their signal strength based on the strength of the signal they receive, so if the signal is weak, they'll increase their output accordingly.
Yup, the weaker the signal the more power the send out trying to get good comms with the local mast.
 

TJ Anderson

-
Mentor
Arms
Esteemed
Even if there is a neutral-earth fault downstream, there would still be no leak as long as there is no potential difference between earth and neutral.
If there was a neutral earth fault downstream e.g. shorted together then there would indeed be no PD but there would be earth leakage, it will parrallel the neutral return current through the cpc. If RCD protected then that would trip from the L-N inbalance
 

TJ Anderson

-
Mentor
Arms
Esteemed
4 electrical checks - 3 by BG, last one by PH Jones.
What exactly regarding in depth checks are needed, so I can request these be made.
I feel responsible for tenant, as not fair they are living with RCD tripping constantly, and who knows how long Energy Ombudsman get to resolution, 8 weeks, after xmas!
To be fair, I think the BG spark has done what he can. He has taken Zs to prove effective connection to earth. He has taken IR at 250vdc. He likely selected 250vdc so he could test with loads connected to eliminate both wiring and loads for earth faults. Sensible. He has also ramp tested RCD.

I agree with others that it may well be interference from meter comms mobile being so close to RCD. IIRC the RCD in that board will be an MEM with a functional earth wire it may act like an antennae!
 
Last edited:

Wilko

-
Arms
Esteemed
Hi - From afar I guess we can never solve this, but there are couple more things for an Electrician to look at in my view. Did the BG Electrician actually personally observe the remote test and the tripping RCD? I would be seeking cooperation from the meter company with some more testing. Something like : Standing at the box with main switch, RCD and all circuits on, have the remote test done and observe the RCD trip. Reset RCD and turn all MCBs off and repeat the remote test and observe any trip. Safely remove the outgoing N from the RCD (still leaving all MCBs off) and repeat the remote test and observe any trip.
 

Leesparkykent

Mod
Mentor
Arms
Supporter
Esteemed
I remember a thread on here a few years ago where on a site walkie talkies were the cause of RCBO’s tripping. And I think it was the same thread where @GMES had the same or knew someone who had the same issue with over 300 RCD sockets and walkie talkies.
 

Strima

-
Arms
Esteemed
You need to find someone with an electromagnetic radiation tester to see what the meter output is.
 
O

Octopus

Probably not the kind of advice I should be posting on the publicly viewable forum but I'd either relocate the meter a greater distance from the CU or I'd wrap the CU in thick tin foil with a bonding wire attached to it and see if the nuisance tripping stops. Obviously isolate, and do a risk assessment first etc.

Smart meters can have fairly powerful WAN transmitters and even GSM transmitters which could cause issues with RCD's if in very close proximity.
1. The CU is in a daft place - and shouldn't really be in the meter cupboard
2. Would changing it to a AMD3 board help
3. Could the SM be disabled for a set period to see if the tripping stops?

Interesting thread..........
 

freddo

-
Arms
Supporter
Esteemed
The communications parts of those meters are in the top grey section of the meter as a plug in module, so it is positioned as close as it possibly can be to the RCD.

Perhaps another reason not to have a smart meter fitted!
 
  • Thread Starter Thread Starter
  • #34
Hi - From afar I guess we can never solve this, but there are couple more things for an Electrician to look at in my view. Did the BG Electrician actually personally observe the remote test and the tripping RCD? I would be seeking cooperation from the meter company with some more testing. Something like : Standing at the box with main switch, RCD and all circuits on, have the remote test done and observe the RCD trip. Reset RCD and turn all MCBs off and repeat the remote test and observe any trip. Safely remove the outgoing N from the RCD (still leaving all MCBs off) and repeat the remote test and observe any trip.
@Wilko
Yes, BG actually observe top-ups causing trip.
Re: Remote Testing - E.org electrician change SM-tripping worse, but he could not touch CU/domestic side. So as per Wilko above, E.org electrician himself suggested that if I got an Electrician out that day, the two could work together - he work on the SM, while my man work on CU/domestic side. PH Jones electr1.ician comes and E.org electrician not contactable! PH Jones confirm 4th time, domestic side all ok.

@Murdoch
Re: On Demand test - yes, every time E.org did test while I on call with them, RCD trips
1. Yes, CU is in daft place
2. AMD3 board help - no idea as I am ignorant
3. I suggested replace SM with Dumb meters but E.org rejected idea, unless I pay cost. But, will ask Monday if they can remotely switch off SM and make it Dumb Top Up

Pictures below CU open
Only RCD - red middle switch trip
Also, tenant tells me today, that when trip happens - Plug circuit all off, But Light circuit stay on (lights work).
elecforum CU Red.jpg elecforum CU.jpg
 

marconi

-
Mentor
Arms
Esteemed
Ines Spires: Some thoughts:

1. Box in the area beneath the consumer unit and place some security seals so that it is obvious if anyone has attempted access.

2. Demand from the energy supplier confirmation that the anti-tamper features of the Secure Liberty 100 are working correctly and that the meter is not suffering from spurious tamper alerts. Are they receiving tamper alerts? Ask them what happens if a single tamper alert is reported to them; does it simply log the alert or is the supply shut off briefly and then restored. If there is a series of tamper alerts what happens?

3. Real tamper alerts are covered by (1) above.
 

Taylortwocities

-
Arms
Esteemed
Also, tenant tells me today, that when trip happens - Plug circuit all off, But Light circuit stay on (lights work).
Of course. It’s only the sockets (to the left of the RCD) that are protected by the RCD.
The circuits to the right of the RCD do not have RCD protection. Don’t know why the labelling has been crossed out.
 
  • Thread Starter Thread Starter
  • #38
Ines Spires: Some thoughts:

1. Box in the area beneath the consumer unit and place some security seals so that it is obvious if anyone has attempted access.

2. Demand from the energy supplier confirmation that the anti-tamper features of the Secure Liberty 100 are working correctly and that the meter is not suffering from spurious tamper alerts. Are they receiving tamper alerts? Ask them what happens if a single tamper alert is reported to them; does it simply log the alert or is the supply shut off briefly and then restored. If there is a series of tamper alerts what happens?

3. Real tamper alerts are covered by (1) above.
1. and 3. A second E.org electrician came after I demanded a Deadlock Letter. He did not change the new SM but did the following "removed the old anti tamper block and installed new 1 and 2 tails" as a free complimentary service. Not sure what that means. Picture below is before he did remove and install.elecforum Liberty 100 SM next to RCD.jpeg
 

marconi

-
Mentor
Arms
Esteemed
Ines Spires: Further thoughts for what you might ask the energy supplier.

1. Is the enclosure containing the consumer unit and meter made of metal? With the door (is it made of metal too?) shut the meter will/may have a difficult time transmitting and receiving signals, especially if the cellular network coverage is relatively poor at the property. Ask the energy supplier what the meter is programmed to do if there are no signals received from the meter or if the meter does not receive any signals for a 'prolonged' period? Ask this because inside the Liberty 100 is a big switch which is normally 'on' but can be turned off either remotely or by the computer inside the meter.

2. Find out what happens if the credit available in the meter runs out. Does the meter cut off or the supplier remotely cut off the electricity supply? What I am wondering is whether the App top ups are not being received by the meter (or intermittently) so the meter runs out of credit and turns off the supply which causes the RCD to trip. But you said the lights stay on - so maybe there is a brief turning off of the the supply until the new credit is loaded or there is a reserve amount of limited credit which kicks in sufficient to keep the electricity on a little while until the meter is topped up so folk are not plunged into darkness. If there is a problem with cellular reception and the meter is inside a metal box then it could be the tenants have paid for a top up but the meter only receives it when the enclosure door is opened to reset the trip.

3. Ask your tenants by how much they top up the meter - large or small amounts. Then consider (2) above.
 

Wilko

-
Arms
Esteemed
... If there is a problem with cellular reception and the meter is inside a metal box then it could be the tenants have paid for a top up but the meter only receives it when the enclosure door is opened to reset the trip.
Monday morning brilliance !!!
Not to make fun of the hardships endured by folks because of this fault, but your thought did remind me of those silly slapstick films ...
 

Reply to Smart Meter Tripping RCD in the Electrical Forum area at ElectriciansForums.net

Electrical2Go - Online Electrical Supplier
This official sponsor may provide discounts for members

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Wetroom Store - Network Wetroom Suppliers
This official sponsor may provide discounts for members
Top Bottom