Ines Spires

EF Member
Thought I would throw my tenant's problem regards Smart Meters (SM) into the mix, in the hope someone could maybe suggest what is going on?

May 2016 - tenants switch to E.org - no problem.
March 2017 - had Liberty 100 PAYG SM (top-Up via App) installed and immediately the RCD/fusebox starts tripping intermittently - every few hours, every day, after few days - see picture.
April 2017 - I contacted E.org and they stated that SM not cause switches to trip, fault is fusebox. Accept what they say.

Tripping continues and tenants check and monitor if appliances causing problem. None found.
BG electricians check home electrics 4 times and state domestic side and RCD all ok - Dec 2017, Aug 2018, Sept 2018 and Oct 2018.

After much elimination find Cause???!!!
Customer Top Up - when tenant tops up via app and then a few minutes later credit shows up on phone, then RCD immediately trips.
Supplier reading - after informing E.org about above and they do On Demand reading from their end, then RCD immediately trips.

E.org change SM Oct 2018 and tripping now worse.
BG check after SM change and state domestic side and RCD all ok.
E.org state that fault is RCD as have changed SM and thus are insistent they are not at fault.
BG believe it is SM, so I am between a rock and hard place.
Requested E.org replace SM with Dumb Meters as a way of eliminating or confirming SM is cause of tripping, but will only do if I pay.

Now starting case with Energy Ombudsman… And tenants’ life not good as now 3/4 times a day have to reset RCD.
Any ideas/advice?

Liberty 100 SM next to RCD.jpeg
 

Murdoch

Electrician's Arms
Get a local independent spark through recommendation to check it out

It’s hard to believe that topping up a meter can trip a rcd

Have you got a picture with the fuseboard cover open so we can see the breakers?
 

spinlondon

Forum Mentor
Electrician's Arms
Trainee Access
Theoretically, there should be reason that the meter can cause a downstream RCD to trip.
 

Marvo

Admin and gender confused
Staff member
Admin
Probably not the kind of advice I should be posting on the publicly viewable forum but I'd either relocate the meter a greater distance from the CU or I'd wrap the CU in thick tin foil with a bonding wire attached to it and see if the nuisance tripping stops. Obviously isolate, and do a risk assessment first etc.

Smart meters can have fairly powerful WAN transmitters and even GSM transmitters which could cause issues with RCD's if in very close proximity.
 

johnduffell

Regular EF Member
the only way to cause an imbalance on a downstream RCD is to cause a leak from one of its outgoing live conductors. Even if there is a neutral-earth fault downstream, there would still be no leak as long as there is no potential difference between earth and neutral.
If the smart meter could cause a change the potential on the neutral above earth, it would cause an imbalance in the presence of a N-E fault.
Has someone actually IR tested the neutral bar with main switch off to the MET with the main earth and all bonding and cpcs connected?
 

Murdoch

Electrician's Arms

Murdoch

Electrician's Arms
the only way to cause an imbalance on a downstream RCD is to cause a leak from one of its outgoing live conductors. Even if there is a neutral-earth fault downstream, there would still be no leak as long as there is no potential difference between earth and neutral.
If the smart meter could cause a change the potential on the neutral above earth, it would cause an imbalance in the presence of a N-E fault.
Has someone actually IR tested the neutral bar with main switch off to the MET with the main earth and all bonding and cpcs connected?
I’ve given you a disagree because lose connections on the supply side can and do trip rcds
 

Ines Spires

EF Member
Will request tenant send me pic with fuseboard cover open. And reason taken so long from initial problem starting immediately when change to SM in March 2017 and going to Energy Ombudsman now is that we also could not believe top up cause RCD trip - but it is true! Also, please see below BG report picture from 11 Oct 2018.

elecforum BGReport.jpg
 

Murdoch

Electrician's Arms
I disagree with faulty meters...
 

johnduffell

Regular EF Member
I’ve given you a disagree because lose connections on the supply side can and do trip rcds
Agree completely, that's why I said "cause an imbalance" because I know there are other ways to trip an RCD.
I just wanted to get the obvious question about whether it was tested properly out of the way!
Given the BG guy has written "power trips out" which is useless without saying what trips (presumably the RCD), I wouldn't be sure they had an eye for precision.
 

Electrician Talk

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Electrical 2 Go - Electrical Supplier and Electrical Wholesalers
Electrical Insurance
ElectriciansForums.net (formerly known as ElectriciansForums.co.uk) was setup in April 2006 to provide free electrical advice to both professional and DIY electricians. Whether seeking advice for auto electrics, trying to find electrical installation condition reports (EICR) form downloads, or whether you're here just to talk to other electricians; we've been a first-choice website for tens of thousands of sparkies for well over a decade.