1.5mm cable, 10A MCB ( or a very thin nail ). label socket " DVR only "
 
Without looking in the BGB/BRB i would say yes, normally a 1.5 twin can carry 19amps

Putting it on a 16a breaker will stop any equipment being plugged in that will overload it and DAMAGE the cable

however as good practice i always use 2.5 twin for most socket outlet work, the odd occasion requires 4mm
 
all depends on what bits are on the van. a 5m length of red/black from a strip-out comes in handy
 
I would also use 2.5 if possible - there's technically nothing wrong with what you're suggesting apart from being a little unconventional, but as mentioned someone may want to use it for something else in the future, or add to it.
 
is it a single socket or a double, if a single its limited to 13A anyway so 1.5 will be fine.
 
2.5mm or a 6amp mcb and a big lable at socket as some smarty might try n use it for a hoover or if dvr posistion is moved
 
1.5 is the minimum for a radial socket taken into account diversity as the plug will be protected by a 13a fuse,
 
Standard practice is to calculate the design load, choose a cable which has a rating equal to or greater than the design load and then choose a protective device that has a rating lower than or equal to the rating of the cable.
 