This suggestion that there is a break in the ground rod connection puzzles me a lot. An open-circuit or high-resistance neutral on a polyphase or split-phase supply can result in both increased and decreased voltages at single-phase loads since the symmetry is lost. But if the symmetry is so poor that a 120V outlet receives 180V when the local ground rod is disconnected, the rod must be carrying a significant part of the neutral current and the neutral / MEN / CNE conductor must already be broken or high resistance somewhere upstream.
In the UK this would be considered a highly dangerous situatiion, where we would advise the customer to switch off and wait for the power company to fix the problem on their side. They would attend immediately and have been known to dig up the road there and then, because of the severity of the danger. Is this not the case in the USA? Would they consider it acceptable to rely on the customer's ground rod to hold the ground and neutral from drifting more than 50V away from where it should be?
Of course, if the neutral and ground are not linked in the consumer's installation, there is no relationship between the outlet voltage and the ground rod connection, so I am assuming Megawatt inferred that in this case the two are connected.