I don't have a clue how to display a SPD on an EICR
Any examples or what fills in where 61643-11
Has two parts Pe-N and L and type T2
 
It isn't a protective device as such so it doesn't need adding to the schedule as an item.
 
Because it's taking up 1 or 2 ways I always describe it as a piece of permanently attached equipment, like a bell transformer, timer or contactor. It ought to have an MCB to protect its cabling (some manufacturers state OCP is not required, but that's unwise and prevents testing if you are in an installation that bothers to test their SPDs when their LPS is inspected). In that case you get to mention the circuit on the circuit chart.

Otherwise I just fill the ways with "SPD" and "61643-11" and "N/a" the circuit tests. At least you can then capture that the cable sizes are correct, and you have a way number to use in the Obs if there is something to note (like the classic "poor install, earthing conductor too long")
 

OFFICIAL SPONSORS

Back
Top