Cheers for the help guys,

If I decide not to fuse the spur and work on the fact that the calculations show the cable is adequate for the 26A + the light, should I just note it on the Minor works certificate and be done with it? I wouldnt be recording on a certificate work that i know damn well doesnt comply , you're just leaving yourself open for a kicking if it all goes pete tong.

Realistically if I fuse down the whole spur, the chances of it blowing are pretty much nil, but it just seems a bit pointless if the cable is always going to be fine. it doesnt matter if the cable is 95mm - standard circuit arrangements limit 1 unfused connection point for each spur.

Being an understairs cupboard it's not like anyone will be changing the simple pendant for a fancy 5x100w bulb chandelier or anything! very true , but we all know you're trying to justify a design decision that just isnt right.

what are the chances of this kitchen socket using more than 13a after being fuse down ?
what is being plugged into this socket now ?
if very little then just fit the extra fcu and stop dithering ;-)
 
Last edited by a moderator:
Have I read this wrong or are you saying that the total for a double socket-outlet is 26A and not 13A?

- - - Updated - - -

Have I read this wrong or are you saying that the total for a double socket-outlet is 26A and not 13A?
 
I just can't understand why a FCU is being tried to be left out. Surely as per the regs (although I'm qualified spark - I am still learning and happy to receive advice) a FCU is required??!
But on a side note surely you would want to switch the light off?? The method you plan to use would mean your light would be on 24/7!!
I would much prefer to fit a FCU as you'd get protection, discrimination and also a means to switch on and off.
 
The method you plan to use would mean your light would be on 24/7!!

How on earth do you work that out?!

Why on earth would I fit an unswitched light fitting?!

I was just curious about the regs regarding spurs as I was planning on adding a tiny load to a spur, which could only ever draw 26A or less and which was capable of taking 27.5A.

It seems that on this occasion the regulations are too restrictive... The 2.5mm T+E cable is capable of carrying the worst case scenario load of the double sockets, plus the maximum that could be draw by my addition of a light fitting. I just don't get why the regs insist on fusing in this case, when it would restrict the cable to less than half its capacity.

I know the regs are there to stop idiots chaining multiple double sockets from a single spur, I just don't see why there isn't something which allow the sparks to do the calculations and make the decision for themselves!
 
Thinking about it, ANY spur on a normal (I mean, 30-32 Amp protected) ring final isn't really very safe according to the regulations...

A single run of 2.5mm T+E can take 27.5 amps maximum... Seeing as most RFCs are protected by a 32A mcb or 30A fuse, it means in the event of a wiring fault the spur could be overloaded with no trip!

A 2.5mm radial on a 32A mcb wouldn't comply with the regs, so why does a 2.5mm spur from a ring final? Is this the only time when an mcb does NOT have to protect the cable in a worst case scenario? If so, why?!
 
Forward fusing DNS,

Each plug has only a max capacity of 13A (the fuse in the plug)
 
Last edited by a moderator:
Thinking about it, ANY spur on a normal (I mean, 30-32 Amp protected) ring final isn't really very safe according to the regulations...

A single run of 2.5mm T+E can take 27.5 amps maximum... Seeing as most RFCs are protected by a 32A mcb or 30A fuse, it means in the event of a wiring fault the spur could be overloaded with no trip!

A 2.5mm radial on a 32A mcb wouldn't comply with the regs, so why does a 2.5mm spur from a ring final? Is this the only time when an mcb does NOT have to protect the cable in a worst case scenario? If so, why?!

Hence why only one spur is allowed, therefore meaning even a double socket with 2 kettles in could pull 26A! The socket would give uip first!
 
On a few domestic test I have come accross a few spur on spurs for 2 tiny load i.e. boiler and condense pumps and turned a blind eye. However I wouldn't do it myself
 
The difference between a spur and a radial on 2.5mm is, a spur = 1 double socket (max 26A), a radial many double sockets @ potentially 26A each.

The fuse in the plug/s protects the cable for the spur, which as SS said above, is why you are only allowed the one.
 
Last edited by a moderator:
With regard to spurs,
I seem to remeber someone on here putting it that -
Your Short circuit protection is provided by the 32A MCB
Your overcurrent protection is protected by the bs1362 fuse.

So is wiring a 2.5mm radial to 1 Socket protected by a 32A MCB O.K. as well :cool3:
 