So is wiring a 2.5mm radial to 1 Socket protected by a 32A MCB O.K. as well :cool3:
Surely it must have a FCU.
I appreciate the additional load will be negligible, the lighting spur, (1.5 = 20 A/ 1.0 = 15.5A) would easily take the load of the LED light, but what about fault conditions?
If it is on a 32A MCB, it would need additional protection.
BS7671....atatutary or non statutary please...come on, quick as you like...I just can't understand why a FCU is being tried to be left out. Surely as per the regs (although I'm qualified spark - I am still learning and happy to receive advice) a FCU is required??!
But on a side note surely you would want to switch the light off?? The method you plan to use would mean your light would be on 24/7!!
I would much prefer to fit a FCU as you'd get protection, discrimination and also a means to switch on and off.