Discuss SSR relay problem solution in the UK Electrical Forum area at ElectriciansForums.net

To what is the round orange panel lamp on the left of the controller connected?

what is the purpose of the round silver knob to the left of the round orange panel lamp? Is it a timer?

Is the clicking sound from the controller?
 
To what is the round orange panel lamp on the left of the controller connected?

what is the purpose of the round silver knob to the left of the round orange panel lamp? Is it a timer?

Is the clicking sound from the controller?
The round red light that flashes is that of the heating, when it is on the heating is on, when it goes off it is because the controller does not send current to the SSR relay and consequently the heating light does not turn on either. The square light you see instead is a two-pole switch. The round knob is a switch-off timer which, if set, switches off the heating for a set amount of time. The noise you hear I believe is the controller, the light or the SSR relay I don't think they can make noise.

I read the previous message, if I put the AT on and set the temperature to 800 degrees, it could be that even after several hours the AT never turns off.
 
Yes. It could take several or many hours for the AT to tune successfully. But, even after a very long period, the AT as designed and implemented inside the controller might be unable to home in to the best values using its trial and error approach to tuning. In which case we leave AT off and use the figures I said to use and adjust them over the life of the oven until we are satisfied with the performance. Auto tuning algorithms are not perfect in all applications.

I must repeat that you have to allow AT at least 3 hours from when the oven first reaches 800C to attempt tuning and ideally longer say 6 hours. At the moment AT may not complete because you turn the oven off too early.
 
Last edited:
Yes. It could take several or many hours for the AT to tune successfully. But, even after a very long period, the AT as designed and implemented inside the controller might be unable to home in to the best values using its trial and error approach to tuning. In which case we leave AT off and use the figures I said to use and adjust them over the life of the oven until we are satisfied with the performance. Auto tuning algorithms are not perfect in all applications.

I must repeat that you have to allow AT at least 3 hours from when the oven first reaches 800C to attempt tuning and ideally longer say 6 hours. At the moment AT may not complete because you turn the oven off too early.
I did the test by leaving the oven on and waiting for more than 6 hours after reaching 800 degrees. The lights of the AT were still flashing, the AT unfortunately did not work.
 
I conclude that AT will not work for your oven. We have tried to use it many times without success. Turn it off and just use the controller with a setting of 800C. Please tell me how the oven performs and allow an hour after reaching 800C.

AT makes some assumptions about the system (your oven) the controller drives. It may well be your oven does not satisfy one or a few of these assumptions which means trial and error does not home in on better and better values for P and I and the other variables.
 
Last edited:
I conclude that AT will not work for your oven. We have tried to use it many times without success. Turn it off and just use the controller with a setting of 800C. Please tell me how the oven performs and allow an hour after reaching 800C.

AT makes some assumptions about the system (your oven) the controller drives. It may well be your oven does not satisfy one or a few of these assumptions which means trial and error does not home in on better and better values for P and I and the other variables.
Good evening marconi, for about 10 days I'll be away, as soon as I'm back I'll do the tests you requested and I'll put the results on the forum, as always thanks for your help :)
 
I conclude that AT will not work for your oven. We have tried to use it many times without success. Turn it off and just use the controller with a setting of 800C. Please tell me how the oven performs and allow an hour after reaching 800C.

AT makes some assumptions about the system (your oven) the controller drives. It may well be your oven does not satisfy one or a few of these assumptions which means trial and error does not home in on better and better values for P and I and the other variables.
Any feedback on this,did we resolve the situation?
Sorry for the absence.

I did the test # 125:

I set the oven at 800 degrees with the AT off and the variables P and I respectively with the values 15 and 160.

Summarizing the values currently present in the oven are the following:

At = No
AL1 = 10
SC = 0
P = 15
I = 160
d = 0
t = 2
rSt = -005
LCy = 0

Test report:

It reached 790 degrees in 2 hours and 26 minutes.

The heating of the oven since I turned it on has always remained active up to 780 degrees, from that temperature onwards it began to switch off and on again quickly, as visible by the flashing red light in the videos I attached in the previous messages.

At 793 degrees the heating started to be on again continuously.

The temperature dropped to 790 degrees despite the heating light was steady.

The temperature rose to 793 degrees and started flashing again.

While the red light was flashing the oven reached the temperature of 796 degrees.

It subsequently started to go down.

When it reached again 793 degrees the red light became steady again.

It began to descend to 790 degrees and then to rise again.

At 793 degrees the red light started flashing again.

The cycle repeated itself continuously without ever reaching 800 degrees.
 
Last edited:
Do you have any connection points in the wiring, do they follow through with the elemental materials of the cable cores? There are so many things you may need to account for, even position of the thermocouple if so you may need to program an offset in to get you to that temp' you seek since now you are in the ball park, of course if you have a wide margin of error it may not matter.
 
set your multimeter to DC volts range so you can pick up 3-32 volts. Connect Positive lead to 3 and common or negative lead to 4. MAKE sure you are reading volts not current....
 
set your multimeter to DC volts range so you can pick up 3-32 volts. Connect Positive lead to 3 and common or negative lead to 4. MAKE sure you are reading volts not current....

We covered that back in the early oart of this thread.
 
New posts

Reply to SSR relay problem solution in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I’m not an electrician and I have a question in relation to Dimplex Duo300n. Some background information: a couple of months ago I have...
Replies
34
Views
7K
Hi, I have been trying to solve this problem for months now. I work as an Electrical Engineer in a tunnel project, we will use TBM machine to...
Replies
13
Views
2K
My view on life, in any field, is not to produce more but to consume less. Everybody told me this is a very eccentric weird mentality. Perhaps...
Replies
12
Views
2K
S
Hi everybody. I am here asking for your help as I am not able to come up with a solution. My system is done this way: I have the main house power...
Replies
9
Views
3K
sampei
S
Please take some time to read through this. It is written by Widdler's father. I found it on a governement website.. It certainly speaks my mind...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock