Control panel attached to the standby diesel generator gets frequently damage despite of earthing of the body and separate grounding of the generator.What might be the causes to damage the control panel of the generator frequently during lightning sound and light rain condition?
only backup generator are effected like control panel issues only .
 
Navaraj: Hello. Your first message is interesting. But to help the Electricians' Forum will need more description by you of the problem, drawings, details of the generator and panel and some photographs of the installation.
 
Last edited:
This is what the OP sent me:

Surge protection device (SPD) is installed at the main utility side.My concern is why only AMF controller panel gets damage during lightning and light rain?
i have attached the picture of the installed SPD.

89830536_2583466788601416_369354517302476800_n.jpg

And my response:

Those look like type 2 surge protectors, at the main incoming supply should be type 1. The manufacturer might be able to provide replacement modules that do both type 1 & 2 in one unit.

Might also be worth looking at installing a type 3 at the AMF. There's some options to choose from here: https://www.dehn.co.uk/en-gb/surge-protection-for-power-supply-systems/type-3-surge-arresters

I'll also post this on the main forum as it may help others.
 
Are there any external control cables to the generator, such as those from an ATS?
If so some appropriately rated SPD on them would help!
 
Navaraj: Could you provide a detailed diagram which shows grounding, bonding and position of surge protection similar to this one:

https://cpower.com/PDF/InfoSheets/44.pdf

Is your installation 'separately derived' or 'non-separately derived' with regards to the neutral neutral?

Is the utility supply overhead from strung overhead bare wires between poles or are the wires insulated and combined into a cable?

1584410272817.png

1584410375805.png
 
Generator is separately driven system with separate neutral earthing system. I I shall provide you some photos of generator AMF panel. 
[automerge]1584454030[/automerge]
Navaraj: Could you provide a detailed diagram which shows grounding, bonding and position of surge protection similar to this one:

https://cpower.com/PDF/InfoSheets/44.pdf

Is your installation 'separately derived' or 'non-separately derived' with regards to the neutral neutral?

Is the utility supply overhead from strung overhead bare wires between poles or are the wires insulated and combined into a cable?

View attachment 56398

View attachment 56399
The installation of SPD at the main supply
 

Attachments

  • IMG_20200317_154104.jpg
    IMG_20200317_154104.jpg
    92.1 KB · Views: 18
  • IMG_20200317_115314.jpg
    IMG_20200317_115314.jpg
    132.3 KB · Views: 19
  • IMG_20200317_092439.jpg
    IMG_20200317_092439.jpg
    75 KB · Views: 20
  • IMG_20200317_105854.jpg
    IMG_20200317_105854.jpg
    121.8 KB · Views: 18
Last edited by a moderator:
What is the line to line voltage of the three phase supply?

Is any surge suppression fitted to the generator supply? If there is please provide a drawing or some pictures.

Some pictures of the changeover switch between utility and generator too please.

Which component in the AMF controller panel is being damaged by lightning?

Last - for now - please post some pictures of the earth/ground electrode(s) - what kind of soil?
 
Last edited:
The line to line voaltge is around 389volt.The surge protection is not used in the standy generator.amf controller damage during lightning condition ,i couldnit identify the damage ,display doesnot work and geneeator doesnot start
Both rod earthing and copper plate earthing is carried out which have an average value of 30- 60ohm per earthing , the soil here present at the side is rocky and soil are not favourable.
Will you please suggest the best earthing ,its type for the worst soil conditon where lightning occur more freqently .
At the main utility site ,transformer neutral earthing is done separately
 
Are your earth electrodes dry - by which I mean simply put into the ground and the original soil and rocks tamped around them? Or has chemical earthing been used which improves the conductivity of the region immediately surrounding the rod or above and below the plates. In Nepal can you buy Bentonite or Marconite ? See:

Marconite | Earthing Compound | Marconite Supplier | Earthing Systems - https://www.powerandcables.com/marconite/

Bentonite | Bentonite, Earthing | AN Wallis - https://www.an-wallis.co.uk/products/earthing/bentonite/bentonite

Are you able to tell me how the utility supply is earthed? TT, TNCS, TNS as explained in the wiki I sent you a link to? I need this information to advise on the Continuous Operating Voltage Uc of the surge suppressors; at the moment they have a Uc of 335V for the Line to Neutral SPs and 260V for the N to PEN.

If Uc = Us the the line to line voltage and one added a safety factor of 10% then Uc would be 1.01 x 389 = 392V which indicates the Uc of the current 'red' SPs is too low at 335V. But until you tell me the earthing system I cannot be more precise.
 
Last edited:
As I said I have been thinking on your problem so more questions for you.

Do you have a transfer switch to connect the installation between utility supply and generator supply? Is it manual or automatic?

What are the approximate lengths of cables - perhaps you could provide a one-line layout drawing which shows the electrical items and the cabling between them. This is relevant because for a short interconnection one surge suppressor could be effective but for a longer length - which can pick up lightning pulses like an antenna - a surge suppressor at each end of the interconnection is probably required.

Similarly all the earth/ground/bonding need to be short and have a high surface area - a low surge impedance; otherwise they present a high impedance to short high intensity lightning pulses which means they are less effective at conducting short-lived high currents to ground and thereby reducing overvoltages occurring at places in the installation where there are sensitive electrical components.

Does the building itself have lightning protection installed?
 