tullynagrow

i have a panel with 2 no star delta pumps 39 kw 63 amps flc can anybody size cable for me length of run approx 100mts 1no pump is on standby but could start if pressure drops the cable has to be afire rated swa clipped to a tray running through an underground carpark the panel has 50 amp motor rated fuses the pumps are to serve a wet riser system eg fire hoses
 
Last edited by a moderator:
i have a panel with 2 no star delta pumps 39 kw 63 amps flc can anybody size cable for me length of run approx 100mts 1no pump is on standby but could start if pressure drops cheers

In a quick answer NO, as you have not given enough info, eg protective device and type, cable run conditions ,is it running through a high temp zone (boiler room) clipped on surface is it in trunking etc.

These are just a few things required before an answer can be given
 
i have a panel with 2 no star delta pumps 39 kw 63 amps flc can anybody size cable for me length of run approx 100mts 1no pump is on standby but could start if pressure drops cheers


in addition to what ian quite correctly said, is it to be calculated as a cyclic load or is it operating only occasionally
 

Reply to star delta motors in the Australia area at ElectriciansForums.net

Similar Threads

Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K
Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi I'm having a problem with a 20 HP pump motor from a hydraulic press to try molds. When we energized the machine, it starts with star...
Replies
8
Views
2K
Hi there, I got a call to a job, table saw (wood) tripping C/B straight away. 4kW motor on Star Delta Starter. So I get to the job, after some...
Replies
2
Views
3K
I've got a call about a pump that is not working. It was a 30 kw motor with a star delta starter. The motor start but before it changes to delta...
Replies
18
Views
6K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock