Hi there,
I got a call to a job, table saw (wood) tripping C/B straight away.
4kW motor on Star Delta Starter.
So I get to the job, after some investigation I find that the main contactor is welded shut and there is a phase to phase short circuit, I find that the motor tails to the windings are shorted together which I found to be caused by loose terminations on the winding side causing the cables to heat up and the lug had melted through the insulation on another phase.

Those tails were cleaned up and tested the resistance, found to all be equal, so the motor was put back in and I put in the replacement contactor, tested the motor side and all seemed okay. On start-up, had a good start on Star but when delta kicks in it would seem I had the phase rotation wrong and an awful noise from the motor, all tripped out, another contactor down.
I get the next contactor and this time confirm rotation by disconnecting the motor tails and using a phase rotation meter and test both sides found my mistake, all sweet, working great without motor connected. Double check the motor at this point with 3.6ohms on 2 windings and 3.7 on the other.

It starts on Star no worries, then I stop because rotation is wrong for saw blade, change rotation at main isolator for machine (my mistake from fault finding).
Go for another start, no go, main contactor A phase dropped. Check motor windings, all the same. I have more contactors on order but I can't keep buying contactors...

Question 1: where am I going wrong?

Question 2: Does it really need to be a star delta starter? It is not a big motor can I just wire it up in Delta?

Question 3: Why isn't the O/L stopping the contactor from burning out? Is the contactor not suitably rated?

Any help or suggestions is much appreciated.
Cheers
 
Question 3: Why isn't the O/L stopping the contactor from burning out? Is the contactor not suitably rated?
Not sure I can add much to what you have done so far, other than a few photos might help folks.

However, the overload side of the contactor is really intended to protect the motor windings against an excessive mechanical load drawing too much current.

What protects (or should protect...) the contactor itself is the MCB or fuses that supply it. Here you would need to check the contactor specification for what sort of protection it needs, and see what sort of protection is actually in use. If there is something drawing a LOT of current, say a short somewhere or the motor being switched direction on star-delta change over, then damage often comes down the to I2t let-through energy of the upstream protection.

There are some motor contactors that have both thermal overload for the motor windings and the equivalent of MCB fault protection built in (forget number but Schneider make them) but even then they are limited to breaking a 3kA fault so you would need to check the PSCC and how any upstream OCPD (fuses, MCB, or MCCB) coordinates with it.
 
Not sure I can add much to what you have done so far, other than a few photos might help folks.

However, the overload side of the contactor is really intended to protect the motor windings against an excessive mechanical load drawing too much current.

What protects (or should protect...) the contactor itself is the MCB or fuses that supply it. Here you would need to check the contactor specification for what sort of protection it needs, and see what sort of protection is actually in use. If there is something drawing a LOT of current, say a short somewhere or the motor being switched direction on star-delta change over, then damage often comes down the to I2t let-through energy of the upstream protection.

There are some motor contactors that have both thermal overload for the motor windings and the equivalent of MCB fault protection built in (forget number but Schneider make them) but even then they are limited to breaking a 3kA fault so you would need to check the PSCC and how any upstream OCPD (fuses, MCB, or MCCB) coordinates with it.
Thank you, in the motor controls I have experience with this has been the usual set up I am used to, apologies for my ignorance. I will have a look at what protection is needed as I believe it was changed recently but this protects the entire machine and an auxiliary circuit, not just that motor. Maybe I should look at a motor circuit breaker to replace the TOL. Thanks for your input!
 

Reply to Star Delta Starter, Blowing Contactor in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hi Guys, We have a CNC router which uses single phase for the spindle, stepper motors and control box. This is all wired in and working...
Replies
10
Views
1K
Hi Changing a 3 phase star delta motor and replacing with a dol 3 phase motor. Would i be right in thinking I can remove 3 of the 6 cables at...
Replies
3
Views
961
Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
378
Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
625
Heeelp! I have an 11kW/21A motor which is attached to a hydraulic power pack. I have replaced the old panels with new, using the same star delta...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock