Hi All
Looking for advice
if anybody’s got any knowledge on static electricity.
been asked to bond flour pipes at work
Do you take it back to the nearest panel or take it to a earth spike ?
 
TL;DR
Static bonding
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members

Pete999

-
Arms
Esteemed
Hi All
Looking for advice
if anybody’s got any knowledge on static electricity.
been asked to bond flour pipes at work
Do you take it back to the nearest panel or take it to a earth spike ?
Have these pipes been tested to see if they are extraneous conductive parts and require supplementary bonding?
 

davesparks

-
Mentor
Arms
Esteemed
Have these pipes been tested to see if they are extraneous conductive parts and require supplementary bonding?
That doesn't matter, the need for bonding to prevent static electricity build up has already been identified.
Whether they are extraneous or not pipes carrying explosive dust such as flour need to be properly bonded to prevent sparks from static electricity causing explosions.
 

Reply to Static bonding of flour pipes in the Electrical Forum area at ElectriciansForums.net

CK Tools :) The professionals choice when it comes to Electrical Tools
This official sponsor may provide discounts for members

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Aico 3000 Range
This official sponsor may provide discounts for members
Top Bottom