I agree with the earth leakage clamp approach to see where the leakage is coming from. Could be cumulative across that many final circuits, without tripping individual RCBOs. I've seen 'normal' leakage on a 7-way board cause a 30mA incomer to nuisance trip, so it's feasible that all your final circuits could do the same to a 100mA. Unlikely, but feasible.
One last thought - I fitted a Lewden (aka Control Gear) 100A 100mA type S a few years ago and kept getting called back for nuisance tripping, when the 30mA downstream never batted an eyelid. All IR tests >99M. I replaced it with an MK type S and never been a problem since. Funnily enough I don't use Lewden RCDs anymore!