Hello all. I have visited a domestic property with two consumer units, one downstairs and then a separate one for upstairs. The upstairs is fed by a 16mm twin and earth and the downstairs is fed by 25mm tails. The cu downstairs is a duel RCD. The question I want to ask is, since the cable feeding upstairs is buried, I was planning to install the sub main directly into downstairs consumer unit. However. The problem is the issue with conflicting RCD. I don't want nuisance tripping occuring since the RCD downstairs is only rated 30ma. I was under the impression that time delay rcbo were easily available but after a bit of shopping around, it's not the case. This was my initial idea on how to resolve the issue. Thank you in advance
 
A time delay RCD is not suitable for the additional protection required for cables buried in walls at < 50mm.
Possible options might be:
1. Add a small consumer unit for the sub main with it's own RCBO, by tapping into the tails before the main consumer unit.
2. I can't think of anything else.
 
With the 16mm T&E buried you simply cannot avoid the requirement for RCD protection at the feed end

You can change the T&E to SWA if its an easy run but apart from that you are stuck with the front loaded RCD
 
It's an annoying regulation. That's why I ran the concealed submain supply cable in my house in MICC.

Is the cable actually buried <50mm from the surface?
 

Reply to Sub main in a domestic property in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
This is a strange one, my neighbour is a bit mad, he had a largish extension built in about 2015, the builder attempted to do everything including...
Replies
3
Views
933
Hey all, I'm looking for some advice to help me troubleshoot my strange issue with my consumer unit/fuse board on which my RCD keeps tripping...
Replies
25
Views
1K
I need to fit a small sub-main board by my service head, to feed a garage unit in an outbuilding. I am thinking of using a Chint shower unit...
Replies
6
Views
2K
I've been carrying out quite a few domestic extension first fixes recently which involves providing a power supply installed from the properties...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock