if its split concentric then the neutral is only really actually single insulated isn't it..... and we normally give single insulated conductors that arent in trunking etc a C2. Imo I wouldn't want to leave it personally
The conductors will only be insulated once regardless - the sheath is there to provide mechanical protection to protect the insulation - not to afford an additional layer of insulation. (That's why Pyro can get away with having an earthed copper sheath - the magnesium oxide only provides one layer of insulation.)

However the neutral conductors in split concentric cable will be both insulated and sheathed. The problem is that there is no guarantee you won't contact neutral (a live conductor) rather than the protective conductor when piercing the cable unlike with SWA.
 
  • Like
Reactions: DPG
I'm sure the last split concentric I came across only had the 1 layer of sheath around the whole thing, I could be wrong it was a while ago
 
I'm sure the last split concentric I came across only had the 1 layer of sheath around the whole thing, I could be wrong it was a while ago
There only will be one sheath. But all live conductors will also be insulated.
 
Inner phase and outer neutrals will be insulated. Earth strands will be bare. I think - someone will hopefully confirm this!
 
  • Agree
Reactions: Richard Burns
Ohh the last stuff i came accross had a single inner core, then a layer of insulation, then the neutral strands, then the outer black sheath.... That was it...
 
  • Like
Reactions: DPG
Isn't that dual-con rather than split-con though?
 
That sounds more like concentric cable rather than split concentric. Split concentric will have the neural insulated and also have bare copper earth strands
 
  • Like
Reactions: DPG
Oh I've not come accross that then haha well i dont see an issue then as long as its booted properly at each end
 
B4A3BC95-EA6B-4FD7-934D-D647EA50F227.gif
Split concentric should be terminated with a 3 finger boot and heat shrink on the conductors.
 
  • Informative
Reactions: suffolkspark

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

polo1

Arms
~
Joined
Location
Glasgow
Business Name
GW Electrical & Security

Thread Information

Title
Sub main protection, views please.
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
29

Advert

Thread statistics

Created
polo1,
Last reply from
stevels4,
Replies
29
Views
2,613

Advert