Discuss Supplementary bonding in the UK Electrical Forum area at ElectriciansForums.net

How does it introduce a C2 on existing instalation in the bathroom?

Because regs say that unless the 3 conditions can be met (main bonding, 30ma rcd protection to ALL circuits, meet disconnection times), circuits have to be supplementary bonded.

Therefore if you install a shower cct. with 30ma protection, you still have to supplementary bond it in order for the non-rcd protected circuits to comply
 
Because regs say that unless the 3 conditions can be met (main bonding, 30ma rcd protection to ALL circuits, meet disconnection times), circuits have to be supplementary bonded.

Therefore if you install a shower cct. with 30ma protection, you still have to supplementary bond it in order for the non-rcd protected circuits to comply

You should find that if it is a copper supply pipe, then it is likely to be connected to the main water bonding anyway. If it is plastic, then it will not be an ECP. Either way, I'm not sure how it will make the other circuits in the bathroom more dangerous.
 
Because regs say that unless the 3 conditions can be met (main bonding, 30ma rcd protection to ALL circuits, meet disconnection times), circuits have to be supplementary bonded.

Therefore if you install a shower cct. with 30ma protection, you still have to supplementary bond it in order for the non-rcd protected circuits to comply

but you don't supplementary bond circuits. you bond extraneous metallic parts. therefore, you have a case inasmuch as any extraneous metallic parts in the bathroom may need supplementary bonding
 
Pretty sure the supply water pipe will be copper, but the plumber hasn't put it in yet
You'll probably find he'll use plastic out of sight and copper for show with lots of push fits more good measure. You just have to IR test to see if it's extraneous or not.
 
But was it not the case that the cpc's of any circuits entering the special location should be bonded, under the 16th edition ammendment?

You are correct in that if the 17th edition criteria are not met, protective conductors of all power and lighting points within zones must be bonded to all ECP's. GN8 does, however, state that cpc's may be used as bonding conductors. Therefore, provided that all ECP's were bonded together either in, or close to the bathroom, and are subsequently bonded to at least one cpc (connected to all the others), then continuity will be guaranteed.
 
Old cylinder cupboard with all pipes bonded together then connected to the CPC of the immersion.

And wasn't it only equipment that was class 1 needed supp bonding anyhow?
 

Reply to Supplementary bonding in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my bathroom there is supplementary bonding of the bath, bath pipework, and basin pipework before it goes into trunking and exits unconnected in...
Replies
6
Views
290
Hello. Non-electrician here. Failed an EICR yesterday as the electrician graded my consumer unit C2. Why C2 and not C3? He didn't say (and still...
Replies
22
Views
3K
Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
5
Views
297
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...
Replies
18
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock