Hi - FWIW I'm not a happy chap if I arrive at a house to find the DB isolator does not isolate the installation. This is where proper safe isolation procedures really could save my life. Let's hope those guys from Pete's Vids never find that place. If I did work on the house I would try my best to not leave it that way. Cheers, David.
 
This installation aside, I've seen and worked on numbers of installations with more than one DB, without one isolator. DB's located in the same position. As Lee stated guidance note 2 gives the guidance, and the above is percectly within the regulations, therefore anything else's which may improve the installation is not required and is just personnel preference and opinion, or have I got that wrong?
Only making the point as someone might read this thread, and consider single isolation as mandatory as regards bs7671.
 
Hi MW, yes I agree. I just reread the OP and now understand the 2 boards are adjacent and labelled :)
 
Yes a building can have more than one installation.
What guidance note 2 doesn't point out, is that the origin of an installation is the customer connection point at the meter.
So a meter with 2 tariffs two connection points, one for normal and the other for off peak would have two installations.
A 3phase meter supplying 3 single phase DBs would have 3 installations.
 