Had a customer today, kettle not boiling correctly, 4th replacement kettle in 3 weeks.
all not boiling past Luke warm

Supply characteristics
TT Supply 66ohms.
No Bonding as caravan and all utilities in plastic (caravan) bonded
RCD protecting caravan and caravan supply (30mA)
when kettle reaches Luke warm it stops boiling (but not click off) then temp drops and kettle brings water back to Luke warm

RCD: 9/15
PFC: 3.25
LN: 245v
LE:244v
NE: 1v

voltage drop: 3volts under load

anyone got any ideas? I am implied to say kettle but how can this be the 4th kettle in 3 weeks?
2nd and 3rd and 4th kettle never worked correctly. 1st worked for 2 weeks

tried different sockets at different locations through the site (garage, new build site supply, caravan)
all under same supply but different CU from same main ISO


Recommended customer to give to daughter to test (some 30miles away)
 
Last edited by a moderator:
same as what he said in his OP

- - - Updated - - -

what wattage are the kettles?
 
resistance is futile .


borg.jpeg
 
  • Like
Reactions: 4 people
Didn't check resistance of element - these are brand new kettles, so didn't think about that sorry
 
Are all kettles the same make and model?
 
Not one of those kettles that have a keep warm function on them is it?? If it is, it could be someone has flicked the keep warm function on so it won't boil, it'll just keep bringing the temperature up to around 80/90 degrees C!! I know because we have such a kettle here!! lol!!
 
  • Like
Reactions: 2 people
All different kettles, non had advanced features like Eco, keep warm or anything.

2 are cheap ones from tesco, one from local shop and one is rustle hobb, only thing similar is they are all base type, no fixed cabled or plug in cable type
 
All different kettles, non had advanced features like Eco, keep warm or anything.

2 are cheap ones from tesco, one from local shop and one is rustle hobb, only thing similar is they are all base type, no fixed cabled or plug in cable type

Unless you have a bad connection on outlet circuit or somewhere, that only shows up under a heavyish load, then your client has had some very bad luck with the kettles they have bought!! lol!!
 
Tried in different outlets on different CUs throughout the same site.
only thing in common is the isolator ourside of the meter, and the cable between meter and isolator
 
Id suggest a loose connection somewhere but if you tried it on different caravans that would be mighty odd! Could you borrow a kettle from another van and try that?
 
try your own kettle in house, customers have tried this on me before any excuse not to make me a cuppa.next they will say they have run out of tea bags and bikkies
 
  • Like
Reactions: 4 people
I would measure current being drawn as kettle is boiling and see if that was close to expected calculated current. If voltage is within correct parameters then you would normally expect current to be what you would expect. Test your own kettle at home then plug it into the caravan socket and see how it behaves. Don't tell the missus though.
 
  • Like
Reactions: 1 person
Presumably you checked voltage was 245 while under load (kettle on)

All new kettles doing the same thing? - it would be amazing to discover all the kettles as being faulty!

Only other possible reason for this would be you are at the north pole and the ambient temperature in the caravan is -50 deg :)
 
  • Like
Reactions: 1 person
Try checking the whole length of the circuit right back to the incomer, if this is the only element they are using it must a high resistance reading on the circuit somewhere.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Supply Problems or very unlucky customer???
Prefix
Forum
UK Electrical Forum
Start date
Last reply date
Replies
19

Advert

Thread statistics

Created
LED Lighting,
Last reply from
Plonker 3,
Replies
19
Views
4,322

Advert