try your own kettle in house, customers have tried this on me before any excuse not to make me a cuppa.next they will say they have run out of tea bags and bikkies
 
I would measure current being drawn as kettle is boiling and see if that was close to expected calculated current. If voltage is within correct parameters then you would normally expect current to be what you would expect. Test your own kettle at home then plug it into the caravan socket and see how it behaves. Don't tell the missus though.
 
Presumably you checked voltage was 245 while under load (kettle on)

All new kettles doing the same thing? - it would be amazing to discover all the kettles as being faulty!

Only other possible reason for this would be you are at the north pole and the ambient temperature in the caravan is -50 deg :)
 
Try checking the whole length of the circuit right back to the incomer, if this is the only element they are using it must a high resistance reading on the circuit somewhere.
 