I need to put a 63A RCB 6 way weatherproof consumer unit ( Garage unit ) with 2x6A , 2x20A , 1x32A MCB's, in my workshop at my farm , now the supply to it, comes from the Main 83A 3 phase fuse box on the other side of the wall where I want to mount this unit , the length of cable would be around 500mm max .

Question , with it being such a short length of cable for the feed could I use a 6mm2 cable ! , as I have loads of it, but no 10mm2 .


cheers


spike
 
There is no ocpd on the supply , apart from the main 3 phase 83A 30mA RCD trip switch coming into the Farm , basicly I am wanting to know if a short length 400mm of 6mm2 cable will take the load of a 63 amp 30mA double pole RCD trip switch .
 
83A rcd is your protection??? So as this isnt an ocpd you must be relying on DNO for ocpd on this submain? i think you need rethink your design, whats the earthing arrangement.?
 
You describe no overcurrent protection at the supply, this would be best before it goes through the wall as otherwise you are relying on the DNO supply fuse which will not be suitable for a 6mm² cable.
The cable is running through a wall so is not in free air, there is a significant limitation to the heat loss.
You have a total maximum load of 84A from the sum of circuit breakers, though this is not the design current.
You are reading the wrong table for the the cable type.

Overall, no, 6mm² cable is unsuitable for this application. Depending on your supply fuse size 16mm² or 25mm² cable would be more appropriate.
 