People don't gland it to the board enclosure because they are too lazy to find a simple solution to do so, just leave it floating in the cavity no one will know is the remit these days.
There's isn't always a cavity to leave it
 
IF I understand correctly - the swa armour is not the cpc or the bonding conductor, but must be connected back to met so that it may act as cpc if required. So at least one connection to met and daisy chained with sufficient ccc to satisfy adiabatic is my thought. This may already be achieved by the trunking but your 10mm will surely do it?
 
Last edited by a moderator:
There's isn't always a cavity to leave it
I know it can be difficult but most things are possible. Entry hole back of board, screw an adaptable box to the rear of it with no lid and use the lid fixing points to fit to the board, gland cable off at adaptable box. Easy peasy on paper and I am already visualizing it in my head:D
 
IF I understand correctly - the swa armour is not the cpc or the bonding conductor, but must be connected back to met so that it may act as cpc if required. So at least one connection to met and daisy chained with sufficient ccc to satisfy adiabatic is my thought. This may already be achieved by the trunking?
If it's not a cpc then it just requires supplementary bonding to earth
 
I know it can be difficult but most things are possible. Entry hole back of board, screw an adaptable box to the rear of it with no lid and use the lid fixing points to fit to the board, gland cable off at adaptable box. Easy peasy on paper and I am already visualizing it in my head:D
Good grief !:)
 
Good point :)
I'm just thinking during the masonry drill attack the armour may be called upon to act as cpc so beef it up ?
Depends as the steel armour conductivity isn't the same as copper so tho you might use a fly lead of 10mm the armour may not be even that equivalent
 
Here..I wouldn't class trunking as an accessory though.

IMG_0484.JPG
 
Na that's if you use conduit say as the cpc and you take a fly lead from the metal back box to the socket as the conduit is the cpc.
In this case the trunking is not acting as a cpc it mearly becomes an exposed conductive part because the swa is glanded to it.
exactly my thoughts or using 2core SWA and the armour as the CPC.
 