Discuss Swa bonding, what method. in the UK Electrical Forum area at ElectriciansForums.net
J
Jason Shawcross
Hi all
Just need your advice, theirs a discussion going on atm on site between a couple of sparks. We have around 50 apartments being fed by 3core swa from a panel room all glanded into the top of a run of trunking, armour isn't used as cpc. One spark is saying we need to run individual 16mm earth's to each gland
Another is saying 10mm to the first of each set and then looping. I would have thought just bonding the trunking near the board adding some bonding tags in-between the trunking sections and bolting the banjos on would suffice. Tbf the trunking is <o.o1 atm anyway to met. So what's your opinion and regs if possible, don't have book with me.
Thank you.
yhink OP's argument is to use the trunking as cpc.
If it's a PME supply then 16mm min for the earth and 10mm min for any bonding needed (can require up to 16mm for bonding if Ze > 0.35 by agreement with DNO, up to Ze of 0.50 if memory serves correct).
The armour being glanded into the steel trunking requires supplementary bonding only if not being used as a cpc in which this situation is not being used as the cpc.
Gland into trunking and link all earth rings together with a supplementary bonding conductor (like 4mm) and take one common supplementary bonding conductor to an earth like the MET or to the panel DB
If the db in the flat is wall mounted and the swa is buried in the wall(masonry or no void) then if your entering the back of the db , it's not always possible it gland the db end.
So gland the supply end.
People don't gland it to the board enclosure because they are too lazy to find a simple solution to do so, just leave it floating in the cavity no one will know is the remit these days.
IF I understand correctly - the swa armour is not the cpc or the bonding conductor, but must be connected back to met so that it may act as cpc if required. So at least one connection to met and daisy chained with sufficient ccc to satisfy adiabatic is my thought. This may already be achieved by the trunking but your 10mm will surely do it?
There's isn't always a cavity to leave it
I know it can be difficult but most things are possible. Entry hole back of board, screw an adaptable box to the rear of it with no lid and use the lid fixing points to fit to the board, gland cable off at adaptable box. Easy peasy on paper and I am already visualizing it in my head:D
IF I understand correctly - the swa armour is not the cpc or the bonding conductor, but must be connected back to met so that it may act as cpc if required. So at least one connection to met and daisy chained with sufficient ccc to satisfy adiabatic is my thought. This may already be achieved by the trunking?
If it's not a cpc then it just requires supplementary bonding to earth
Good grief !:)
Good point :)
I'm just thinking during the masonry drill attack the armour may be called upon to act as cpc so beef it up ?
Depends as the steel armour conductivity isn't the same as copper so tho you might use a fly lead of 10mm the armour may not be even that equivalent
Here..I wouldn't class trunking as an accessory though.
Na that's if you use conduit say as the cpc and you take a fly lead from the metal back box to the socket as the conduit is the cpc.
In this case the trunking is not acting as a cpc it mearly becomes an exposed conductive part because the swa is glanded to it.
exactly my thoughts or using 2core SWA and the armour as the CPC.
Of course it needs to be earthed.
As it's an exposed conductive part who actually said it needs bonding as in extraneous??
I said supplementary bonded to earth or ' earthing ' which is different to protective bonding ,as in extraneous parts
Thing is, even if the armour isn't being earthed at both ends. It still needs glanding. It needs terminating correctly!
I'd sack any "electrician" who thought this was a solution.
An westwood, I'm not saying you think this is correct.
Don't think it is correct at all but it is the nature of the trade now because people do not have skills to engineer solutions.
Earthed agreed. But the use of the term bonding in this sort of thing is the cause of much confusion. It results in people assuming a bonding conductor is there to earth their pipes....such confusion causes many a newbie Electrical Trainee bursting with self importance to berate a plumber for using plastic fittings on copper pipes
It's not following the regs though, everything should be suitably terminated (or words to that effect).
Maybe it's just me, but there seems to have been a huge influx on a few forums all with similar questions. god knows whats going on.
Couldn't agree more Rob.
Hi all
Thank you.
Personally I would use Piranaha nuts (think they do a 32mm size) on each SWA and verifiy that the trunking is solidly bonded. No need for daisy chain links IMHO. What size are the subs?
Reply to Swa bonding, what method. in the UK Electrical Forum area at ElectriciansForums.net
Been looking at a CU change in a small office and would appreciate comments on the following. Office is supplied from the mains intake in the...
6K
I have a metal Hager sub CU, 10 way RCBO, installed in 2018 in an accessible attic space, this sub-CU being fed from another unit close to the...
6K
I'm in Azerbaijan, and in our company store we have a number of drums of cable, all upwards of 5 years old and basically unsaleable. We're looking...
Hi all, I’ve been given 3 flats to re wire and i was looking for advice on the correct size Swa to use. There will be 3 meters installed by the...