Hi,

One of our installers has completed a jobwithout fitting the fibre washers to the SWA CW cable glands.
As such we have been snagged by our client fornot meeting required IP rating.

The system is now operational and there is alarge number of cables and glands.
It is going to be a massive job to disconnect,remove, fit washer and re-gland.

Does any one know if there is anything availablethat will allow us to seal the glands without having to fully remove?
Unlikely I know but need to explore alloptions.

Thanks,

Carl
 
Were the glands IP66? I think CW glands come in different IP ratings what IP rating was specified on that particular installation?. Is the missing washer between the gland and the gland plate?
 
A standard CW gland doesn't have a fibre washer with it, is this something extra your client had specified?

Unfortunately if fibre washers were specified then they probably won't accept anything else. If it is to seal where the gland meets the gland plate/threaded entry you might be able to take a leaf out of the plumbers book and use hemp & sealant in there?
 
Standard gland threads are IP54. The use of a thread washer (normally red fibre or nylon) increases the ingress protection to IP66. What IP rating did the client specify? If they specified an ingress protection rating of IP66 and the use of a washer to achieve it then unfortunately it looks like you will have to install the washers.
 
All,

Thanks for your responses.

The glands fitted are CW type (IP54).
Our clients specification is that IP ratingmatches that of the equipment it is glanded into (in this case IP65 junctionboxes).
To reach IP65 we have to fit the washers (or asI had hoped an equivalent).

Unfortunately verification was done by a thirdparty (who won’t be used again) and this was not picked up.

We are going to have to bite the bullet anddisconnect all cables and fit fibre washers.

Thanks again for all your suggestions.

Kind Regards,

Carl
 
All,

Thanks for your responses.

The glands fitted are CW type (IP54).
Our clients specification is that IP ratingmatches that of the equipment it is glanded into (in this case IP65 junctionboxes).
To reach IP65 we have to fit the washers (or asI had hoped an equivalent).

Unfortunately verification was done by a thirdparty (who won’t be used again) and this was not picked up.

We are going to have to bite the bullet anddisconnect all cables and fit fibre washers.

Thanks again for all your suggestions.

Kind Regards,

Carl

Oh dear! How many glands?
 
All,

Thanks for your responses.

The glands fitted are CW type (IP54).
Our clients specification is that IP ratingmatches that of the equipment it is glanded into (in this case IP65 junctionboxes).
To reach IP65 we have to fit the washers (or asI had hoped an equivalent).

Unfortunately verification was done by a thirdparty (who won’t be used again) and this was not picked up.

We are going to have to bite the bullet anddisconnect all cables and fit fibre washers.

Thanks again for all your suggestions.

Kind Regards,

Carl

Carl, CW glands are IP66 rated.
Are these junction boxes threaded cable entry holes or clearance holes?
If you have more than 5 threads or 6mm engaged then the IP sealing washer may not be required.
I know that a standard pack of CW glands do not come with sealing washers but still state IP66 on the pack due the seal of the back nut of the gland.
I do come across this scenario often while carring out periodic inspections on ex rated equipment.
What brand of glands have been used and what make of junction box?
Also, avoid red fibre washers and go for nylon if it turns out they need fitting after all.
 

Reply to SWA CW Glands - Sealing Advice in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi All. What is the best/preferred method when connecting 20mm conduit to a back box of a socket on an outside wall ? I am connecting a BG...
Replies
10
Views
3K
Hi all, My first post here, thought I'd see if it was possible to get some advice or tips... Basically, I had a large amount of block paving and...
Replies
80
Views
12K
Background: Served my apprenticeship 1964 to 1969 with NORWEB but not been directly employed in the industry since then. I have just laid a 10mm...
Replies
27
Views
9K
Hello all I'm doing a Job in France for my company where we are installing SWA for power to our own control panels The issue is the DB is a...
Replies
46
Views
9K
Silly Sausage
S
Im seeking advice from a job we have done with the most difficult customer of my whole career. We're a family business of 50+ years and take pride...
Replies
81
Views
11K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock