Hi wondering if someone can help, I left my BRB in my office and stuck on job trying to work out a few things.


I need the CCC of 16mm flat SWA 2 core cable, armoured is takin earth from meter cupboard to flat on 2nd floor. roughly a 15m run as its already a exisiting installation, it grouped with 5 other supplied feeding other flats from there own independant switch fuses....
Main system is TNCS PME... Ze at switch fuse is 0.09 Ze at CU 0.12.

But my client has decided to get her builder in to refurbish the bathroom and already plumbed in a wacking 9.5kw shower (41amps) so a 45 amp mcb needed for this, then decides to call me in to connect up power to it and change board....


She got 32a cooker mcb, 32amp for ring, 16a for standby immersion, 6 amp for lighting.....and now a
My concern is the CCC will be able to cope with her new max demand of approx 79 amps
32+32+16+6 x 0.4 + 45 = 79.4


I already have one issue with her old MEM 60amp (Ceramic Rewireable) switch fuse that needs upgrading to at least 80amp.... (In main meter cupboard) EDF have given me permission to change this, but im assuming the main switch is rated 60 amp too so there fore EDF have got to change it as its tails are from meter.

But my main issue is the CCC of the existing SWA.


Cheers guys sorry if some dont make sense, written really quick on mobile....
 
Well I would apply the grouping factor (Cg) of 0.60 which gives an Iz of 89 x 0.60 = 53.4A


This is obviously based on the 5 cables touching, not on a tray or ladder and more or less equally loaded.

There may be other factors such as insulation properties, temperature, and you also mention a re-wireable fuse which has it's own factor, but you are changing that.
 

Similar threads

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread Information

Title
Swa flat cable help
Prefix
N/A
Forum
Australia
Start date
Last reply date
Replies
4
Unsolved
--

Advert

Thread statistics

Created
danny124,
Last reply from
danny124,
Replies
4
Views
1,649

Advert