Hi All,

I've been asked to get a supply for a car park PIR light across the car park entrance from the existing light. The only way across would be by running the SWA cable in a drain that runs across the driveway (see picture).

Is there any reason that I shouldn't do that? I can't think of any regulation of the top of my head that prohibits it.

TIA

HOJpPu4ERieQsG7d7xtvvg.jpg +KLbPQMwTt6IHHEQfCx+IA.jpg
 

telectrix

Scouser and Proud.
Respected Member
Forum Mentor
Electrician's Arms
CCTV / Alarms
Solar Guru
Trainee Access
DIY
is the drain likely to be dug into with a spade?
 

Ian1981

Forum Mentor
Electrician's Arms
Trainee Access
A drain is for drainage and not for cable runs as far as I’m concerned.
It’s a bit rough I’d say as I don’t like the idea of water in contact and maybe covering the cable.
Also proximity to other services although not water pipes I wouldn’t do it.
 

pirate

Regular EF Member
Compacted debris will build up over time, and traffic will compress it into the SWA...sharp gravel, sand, general grit and debris...doesn't look like a great idea...
however, running it in a steel conduit?
 

telectrix

Scouser and Proud.
Respected Member
Forum Mentor
Electrician's Arms
CCTV / Alarms
Solar Guru
Trainee Access
DIY
maybe run it in some heavy gauge plastic ducting.
 

westward10

In echoed steps I walk across an empty dream.
Staff member
Moderator
Forum Mentor
Electrician's Arms
Trainee Access
That is not s drain it is a soak away plus that is not the only way across.
 

Vortigern

Regular EF Member
It looks like that drain is starting to break up anyway. The cement is cracking around it. Not a good future for the cable. Maybe use it and dig deeper than. But regs say 450mm don't they?
 

Colin33

Regular EF Member
I'd be tempted to break out the concrete one side of that drain, lay the swa in some plastic ducting, then concrete over. You may find that existing concrete breaks out really easily, and at least then the cable can be withdrawn/replaced easily in the future.
 

Gavin John Hyde

Electrician's Arms
CCTV / Alarms
why not just whack a pole in the ground and put a solar powered one on it? the council have been fitting them around here in the car parks and park and rides. give out a good amount of light too , the solar panel is not too large either.
 
Last edited:

Wilko

Electrician's Arms
Hi - I wouldn't do it - I could reasonably foresee the gully needing cleaning out and or collapsing. And then there's the warning tape ...
 

dksanders

Electrician's Arms
A drain is for drainage and not for cable runs as far as I’m concerned.
It’s a bit rough I’d say as I don’t like the idea of water in contact and maybe covering the cable.
Also proximity to other services although not water pipes I wouldn’t do it.
There are no other services in the drain
 

dksanders

Electrician's Arms
Hi - I wouldn't do it - I could reasonably foresee the gully needing cleaning out and or collapsing. And then there's the warning tape ...
isn't warning tape only required when the cable is buried? as the cable would be sat in the bottom of the concrete trench and protected by the cast covers, it's totally visible.
 

Electrician Talk

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
Electrical 2 Go - Electrical Supplier and Electrical Wholesalers
Electrical Insurance
ElectriciansForums.net (formerly known as ElectriciansForums.co.uk) was setup in April 2006 to provide free electrical advice to both professional and DIY electricians. Whether seeking advice for auto electrics, trying to find electrical installation condition reports (EICR) form downloads, or whether you're here just to talk to other electricians; we've been a first-choice website for tens of thousands of sparkies for well over a decade.