Yes, Table 54.8 is only applicable where PME (TN-C-S) conditions apply.
For TT, and TN-S sytems, there is no requirement for a copper equivalance.
 
That applies where the bonding conductor is required to have a CSA greater than 25mm².
 
That applies where the bonding conductor is required to have a CSA greater than 25mm².

It may read that way, GN8 gives a clear explanation and equation for the requirements of bonding, page 41
 