Discuss SWA r1r2 35mm ... ..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Judd

-
Reaction score
59
Could anyone give r1r2 values per metre for 3core 35mm SWA also incorporating the armour as a protective conductor?

The figures I've obtained are 0.00282 but I'm unsure if this incorpartes the armour.

It's to supply a bungalow but the meter and cut out is 160 metres from the house itself.
Thankyou
 
im going from memory here but I get 0.53 Ohms at 160 meters without factoring conductor operating temp at 70 degrees which would be roughly 0.64 this is a proper smoke packet calculation though.
 
I'm going to measure ze tomorrow would anyone be willing to help me with my calculations?
Originally Sp energy where going to supply to the house, somewhere along the way but after I had started the rewire of the property the owner decided to supply his own cable and feed it off the meter 160 metres away.
 
Boozey lunch to be noted, so no warranty :) - a single 35mm conductor is 0.524 mOhm/m at 20C (OSG table I1). So for 160m at 20C without armour you should see about 0.169 Ohm when looped. Putting armour in parallel with one leg is = 0.524+(0.524//Armour) mOhm/m. Armour is 70mm of steel (GN1 table D10b) which for disconnection purposes is equivalent to 31mm Cu (same table) or about 8mm Cu for resistance. Doing resistance calc the 8mm Cu is about 2.46 mOhm/m. So I calc the resistance of 160m of looped 35mm and armour (in parallel with one leg) at 20C to be ... 0.153 Ohm ... ha ... maybe. Anyone been drinking too?
 
Hi , if you use the resistance values from cable manufacturers like Batt cables then the resistance of 35mm is 0.524 and the resistance for the armouring is 2.1 .
So 160 x 0.524 x 1.2 (70 degrees ) /1000 =0.10
160 x 2.1 x 1.18 (60 degrees ) / 1000 = 0.39
therefore 0.10 + 0.39 = 0.49
 

Reply to SWA r1r2 35mm ... ..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Evening all. I have a question as I can’t get my head around something with solar PV I’m going to be working on a new build in a couple of...
Replies
9
Views
2K
As you may know looking at some of my posts I've been thrown back in the deep end recently – and don’t have much experience with complicated...
Replies
9
Views
4K
ELECSA Certification Scheme Regulations Clarification (ELECSA Assesment)
Hi All, I have my ELECSA assessment in a few weeks time. I was going to install an in-line water heater at a friends house but am now considering...
Replies
73
Views
9K
Carrying out an EICR and some minor works on a client's flat. This is a grnd floor flat in a converted victorian house. All the services go into...
Replies
19
Views
7K
Engineer54
E
E
I think I've Posted this before, but I've just updated it. Some of the sparks where I work still get a little confused of what the different areas...
Replies
58
Views
77K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock