Unless I am missing something your drawing should function assuming the uv contactor coil is also 415v.
Yes, but you will need a timer with contacts rated to switch 400V.Will this work?
Once there are external control devices and single-phase 230V loads, that advantage of the 400V coil is lost and the need to use 400V rated contacts on everything is very limiting. Hence the preference for 230V or better still ELV controls if a transformer can be justified.
Sure thing, what I meant was that is that one doesn't want 400V coils and control circuits even within a panel, because 400V is harder to switch with small relays and control devices.
What is operating the 400Volt coil, are dry contacts on the 230 timer, somehow integrated into the 400 Volt control circuit, dangerous and I believe does not comply to BS 7671, cant give you the reg number if there is one, it was/is something in the back of my mind that is reminding me. Imagine the problems of a 230 V timer with NO/NC dry contacts, with a possible 400V sitting on them, not nice.On a lot of contactors there is a switch that sets the contactor to stay off in the event of a power failure or restart automatically.
Not sure how 230v will operate the 400v coil though!
Also the UV’s must turn off if the pump stops. They will burn out otherwise.
Where abouts are you?
Do you know the reg number Rob out of interest?Once external controls are introduced. Anything above a 230v control circuit is currently forbidden. It's not just preference, it's regulations.
Thanks Rob Will take a lookSection 9 BS60204
Still come across plenty control panels with 400v control circuits but anything controlling remotely with 400v is definitely a no no.Section 9 also covers this. Any more than 2 control devices and it needs a dedicated isolating transformer or psu.
Can't get much in the way of a control system with that. Hence the only 400v control you really see now a days is the dol in a box with a stop and start button. Even then these usually aren't wired control. Simply pushing the contactor in manually, then hitting the trip on the OL to stop.

Still come across plenty control panels with 400v control circuits but anything controlling remotely with 400v is definitely a no no.