Can anyone point me to the part in the regs that explains when the neutral needs to be broken for isolation.

I'm looking in the case of a three phase sub board main incoming switch - when to use 3 and when to use 4 pole. And isolator switch for fixed appliance, again 3 phase - linked neutral or 4 pole switch.

I seem to remeber that if you have PME this has some effect due to the supplier not been able to guarantee the neutral is at earth potential?
 
Don,t know where you got that from mate, in my personal opinion i think its always better to use 4 pole, as the neutral being a phase conductor i think its better to break it on isolation.
Especially when its an appliance you know you are safe from any feed backs off somewhere else.
 
Can anyone point me to the part in the regs that explains when the neutral needs to be broken for isolation.

I'm looking in the case of a three phase sub board main incoming switch - when to use 3 and when to use 4 pole. And isolator switch for fixed appliance, again 3 phase - linked neutral or 4 pole switch.

I seem to remeber that if you have PME this has some effect due to the supplier not been able to guarantee the neutral is at earth potential?

hi there

look at 537.1.3 / 1.4 etc :)
after all neutral is a live conductor:p

cheers
 
hi there

look at 537.1.3 / 1.4 etc :)
after all neutral is a live conductor:p

cheers

I see what your saying, but 537.1.2 states that in a TN-S or TN-C-S system the neutral conductor need not be isolated or switched where it can be regarded as being reliably connected to earth by a suitably low impedance.

Big spanner in to vital works!!

P.S, just reading down the page it says the same thing again in 537.2.1.1 - neutral need not be isolated or switched in TN-S or TN-C-S.
 
Last edited by a moderator:
As a personal preference I do like to isolate all live conductors, I was merely giving the OP some definitive answers from ol' red as per his query.
 
Thanks for the pointers. It just occurred to having needing a 63A isolator and the wholesaler only having a three pole one in stock.
 

Reply to Switched neutral or not? in the Australia area at ElectriciansForums.net

Similar Threads

5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
Replies
2
Views
493
Hi all.. Bit of a nightmare afternoon,, testing a caravan park TP&N panel board IR testing while board isolated before returning power (merlin...
Replies
5
Views
916
For power outages, my solar inverter (+battery) is able to take on the entire house load - as long as I unplug my collection of vintage kettles...
Replies
3
Views
820
Hi all I am new to this forum and hope this is right placed and of interest. I would like to make a setup with one or more impulse relays...
Replies
9
Views
990
Hi everyone, I want to repurpose an old cable that was previously used to power a 3-phase machine. The cable is 4L1.5 micc, and I don't want to...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock