Hi All,

Another quick one I need clarifying..

i have used some SY I had to connect from a FCU out to a boiler. I used this cable as it was round in profile and fit the gland out of the FCU & cable entry into the boiler better than some T&E.

I have used 4 core and ID'd the colours onto the 3 conductors used, 1 being used as earth, 1 being redundant. Does the braiding require earthing like SWA?

The cable is internal of the building and surface mounted for the 300mm from FCU into boiler.

The circuit is protected by 30mA RCD.

Thanks,

Andy
 
the braid should be earthed using the proper SY glands.
 
That confirms what I thought, albeit after the event. Will be easier to swap it out for T&E or flex!

Annoying as it looks rather nice to my eyes. Lol
 
Its not for out here mate. They don't have armoured or anything out here and just lay flex cables directly on the ground, even if there's vehicle traffic going over it!
 
Gn8 states that the armouring in swa is classed as a exposed conductive part. SY is a similar make up therefore it needs to be connected to earth
 
Yeah earthed, but if your connecting up a boiler shouldn't it be heat resistant flex anyway?
 
Don't get confused here ... its original use was a control wire with screening and in some sensitive set-ups circulating earth currents can occur between the earth core or other earthed metalwork and the screen which can corrupt data, signals and generally cause alot of issues, its these cases you ground at one end. Where in your case your using as power cable it requires earthing and recommended at both ends ... note here is some manufacturers do state that the cable isn't for power cable use and control wiring only.

I wire inverter controlled motors with SY and most specify earthing braid down onto motor and to mount plate on the inverter or separate screen terminal if supplied, those who reel off quotes like screen should only be earthed/grounded at one end should further explain when to and why...more often then not it shows there lack of knowledge about the circumstances in what they say is true.
 
SY cable screen does NOT require earthing although it is considered good practice to do so. If terminated using PVC glands correctly it would not be classed as an exposed conductive part contrary to what you might hear others on here say.
 