Didn't he say he sleeved a core for earth therefore its not used for fault current is it not, so IMO to leave it un-earthed for his situation feeding a boiler WAS THE WRONG ADVICE
I'm not talking about using the braid as THE earth (it can't be anyway), I'm talking about earthing it in general. The fact is, the use he has suggested tells me that the cable is very unlikely to be damaged therefore he could use a flex if he wanted. The braid cannot be classed as an exposed conductive part if it is glanded in PVC at either end. He didn't need to use SY for this situation, I don't even see what the argument is?!?
In this situation the braid is essentially some metal within a cable that cannot be touched, cannot become live under single fault conditions and serves no purpose, so why earth it??