Didn't he say he sleeved a core for earth therefore its not used for fault current is it not, so IMO to leave it un-earthed for his situation feeding a boiler WAS THE WRONG ADVICE

I'm not talking about using the braid as THE earth (it can't be anyway), I'm talking about earthing it in general. The fact is, the use he has suggested tells me that the cable is very unlikely to be damaged therefore he could use a flex if he wanted. The braid cannot be classed as an exposed conductive part if it is glanded in PVC at either end. He didn't need to use SY for this situation, I don't even see what the argument is?!?

In this situation the braid is essentially some metal within a cable that cannot be touched, cannot become live under single fault conditions and serves no purpose, so why earth it??
 
i always earth the sy when connecting motors from inverter. the armouring is not strictly nessicarry most of the time as it usually chucked in the power trunking.
 
We agree on those points regarding SY as rough service but remember other not so experienced members could have read your posts and got the wrong impression which you have had to expand on to explain.

What it comes down to is any cable where the sheath, braid or armour is been used as mechanical protection regardless of been sealed off and none exposed should have it earthed, even if the SY is used in a situation where its beyond its design it should still be earthed ... ive seen SY used as extension cable for 230 and 400v industrial use and on 2 occasions the sheath was found live due to both incorrect use of cable and damage incurred ....had it been earthed sheath at least the risk of injury or death would be limited ... regardless of improper use of the cable.

I did realise you were been hypothetical but the use of SY or misuse is now very common and i believe its just the fact that the regs has yet to catch up and not that it isn't required... sometimes technology moves faster than regulation.

PS i get SY glands about £3 each ....if you dont want to pay £20-£30 quid dont go to RS Components
 
How can anyone tell on a forum how well this chap has terminated the cable in the FCU and or Boiler, is the screen totally isolated from touch by a boiler engineer for instance, I've seen some rough work in my time, earthing it eliminates any danger IMO
 
I have seen exactly the same thing more than twice and I wish I could of typed that as well
We agree on those points regarding SY as rough service but remember other not so experienced members could have read your posts and got the wrong impression which you have had to expand on to explain.

What it comes down to is any cable where the sheath, braid or armour is been used as mechanical protection regardless of been sealed off and none exposed should have it earthed, even if the SY is used in a situation where its beyond its design it should still be earthed ... ive seen SY used as extension cable for 230 and 400v industrial use and on 2 occasions the sheath was found live due to both incorrect use of cable and damage incurred ....had it been earthed sheath at least the risk of injury or death would be limited ... regardless of improper use of the cable.

I did realise you were been hypothetical but the use of SY or misuse is now very common and i believe its just the fact that the regs has yet to catch up and not that it isn't required... sometimes technology moves faster than regulation.

PS i get SY glands about £3 each ....if you dont want to pay £20-£30 quid dont go to RS Components
 
i always earth the sy when connecting motors from inverter. the armouring is not strictly nessicarry most of the time as it usually chucked in the power trunking.

Agree not necessary as mechanical protection but your coming from an inverter then EU regs on RF interference etc means you will normally ground it down both ends dependant on inverter requirements so in this case a bad example as its a functional screening.
 
What it comes down to is any cable where the sheath, braid or armour is been used as mechanical protection regardless of been sealed off and none exposed should have it earthed

I absolutely agree, and this point is not in dispute.

Let's say for example that in a moment of madness I wanted to extend a circuit clipped direct in an area where there would be no need for mechanical protection, I would be well within my rights to use SWA or SY without earthing the armour or braid providing that I didn't create a need for the armour to be earthed, eg' using a brass gland.

Of course I would be mad to do such a thing, but this was my point. In the situation the OP described, he does not need to earth the braid, that is all.
 
How can anyone tell on a forum how well this chap has terminated the cable in the FCU and or Boiler, is the screen totally isolated from touch by a boiler engineer for instance, I've seen some rough work in my time, earthing it eliminates any danger IMO

I wasn't speculating on how he had terminated his SY, merley stating that if he terminated it a certain way, then the braiding doesn't need earthing.
 
I think there will be a lot of headless chickens going around on site tomorrow saying "I don't need to earth the SWA or the braid of an SY cable cause I read it on a forum" they'll be quoting "in an area where there would be no need for mechanical protection" could be high level on a cable tray/ladder tight to the roof lol
 
I think there will be a lot of headless chickens going around on site tomorrow saying "I don't need to earth the SWA or the braid of an SY cable cause I read it on a forum" they'll be quoting "in an area where there would be no need for mechanical protection" could be high level on a cable tray/ladder tight to the roof lol

Is their lack of grey matter my fault?!? Lol
 
Agree not necessary as mechanical protection but your coming from an inverter then EU regs on RF interference etc means you will normally ground it down both ends dependant on inverter requirements so in this case a bad example as its a functional screening.

thats using it just for power though, is it still covered in same regs?
 
I can't believe that any experienced qualified electrician would ''NOT'' earth the braiding on SY or similar constructed cable. As for making a case for not earthing the braiding, i can only think of one such situation...

In most instances where this SY cable has been used on this forum, it has been used in situations that the cable was never designed for, and where even some manufacturers have found it necessary to issue statements to this effect!!
So if you are going to use this cable, use the correct glands which low and behold, incorporate the means to earth the braid, which should be telling those that advocate not earthing something!!!
 
We use a lot of SY cable for power and always use EMC cable glands (mainly from RS). You are going to gland the cable anyhow so you might as well spend a bit extra and call up EMC glands.
The manufacturer of the cable has also stated that their cables can be used for power cables.
 