I have a ring cct (2.5mm ) in my cabin which is protected by a 20amp RCBO. This has been in existence for over 3 years with no issues. I recently bought a table saw and when turned on, on its own all is OK. However the other day I had a heater and a dust extractor on, then turned on the table saw, the RCBO immediately tripped. It only trips when other appliances are on and you turn on the table saw. My question, is there a way to dampen the start up of the tablesaw motor or would I have to upgrade the RCBO to 32amp. The table saw is a Dewalt with a 2000watt motor. It is a bit aggressive on star up. Ideally is there something it can be plugged into to reduce the initial surge it creates.
 
Try starting saw first, dust extractor second and heater last. If the heater is a 2KW fan heater you will be close to the limit without the extra load of starting the motor anyway. Saw , hopefully, when its running will take a much lower current than what its rated at.
 
The simplest solution is probably turn the heater off while sawing!

As the others have said, you are likely pushing the circuit design as heating generally consumes a lot of power. I'd expect if you look at the ratings on the extractor and the heater and add up the power in watts, and then add 2000 for the saw you'll be at over 4600 watts which in simple terms is the peak limit of a 20A circuit, and it shouldn't be running with even this load for long periods.

If you will want these three things on together regularly then you need someone to look at the supply to the cabin (which is the limiting factor) and see what can be done. There may well be simple solutions but a lot more info is needed to say something is safe.

When you say ring circuit, is it actually a complete loop or a more common daisy-chained (radial) socket circuit?
 
The simplest solution is probably turn the heater off while sawing!

As the others have said, you are likely pushing the circuit design as heating generally consumes a lot of power. I'd expect if you look at the ratings on the extractor and the heater and add up the power in watts, and then add 2000 for the saw you'll be at over 4600 watts which in simple terms is the peak limit of a 20A circuit, and it shouldn't be running with even this load for long periods.

If you will want these three things on together regularly then you need someone to look at the supply to the cabin (which is the limiting factor) and see what can be done. There may well be simple solutions but a lot more info is needed to say something is safe.

When you say ring circuit, is it actually a complete loop or a more common daisy-chained (radial) socket circuit?
It's a sub board in a cabin fed by a 10mm swa 3 core, at about 20meters from the main board feed. The cct is a true ring cct wired with 2.5mm cable. Not a radial.
 
I would not be putting a 32a rcbo just because its been suggested by someone I don't know on an Internet site.
A 32a rcbo may be fine or it may be dangerous. You wouldn't know without further tests. I always think there must be a reason why someone has chosen to put a 20a on what seems to be a ring.
The 20a type C suggestion is good, assuming you can get an EFLI result low enough.
 
I would not be putting a 32a rcbo just because its been suggested by someone I don't know on an Internet site.
A 32a rcbo may be fine or it may be dangerous. You wouldn't know without further tests. I always think there must be a reason why someone has chosen to put a 20a on what seems to be a ring.
The 20a type C suggestion is good, assuming you can get an EFLI result low enough.
The 20amp was first used as it was spare and we did not need any heavy loads so it would have been fine. The correct fuse rating for the ring would have been a 32amp RCBO. So fitting one would be OK as it is a true Final Ring cct. However I like the idea of the C curve as I had forgotten about that characteristic.

( For those who may be reading this B Curve RCBOs trip between 3-5 times full load current and are mainly used in residential applications where loads are resistive e.g. lighting fixtures, domestic appliances with low surge levels.
C Curve RCBOs trip between 5-10 times full load current and are intended for high-level overcurrents. They are the normal choice for commercial and industrial applications where fluorescent lighting, motors etc. are in use.)

However I have come across this, and will be installing as it aids the saw as well. A Soft Start Module.

In addition as we may put further power tools in now I think a C curve RCBO will be in order.

Many Thanks for your reply as this has prompted many solutions and my further understanding. It puts me in a much better position when inviting quotes from electricians.
 
I would not be putting a 32a rcbo just because its been suggested by someone I don't know on an Internet site.
A 32a rcbo may be fine or it may be dangerous. You wouldn't know without further tests. I always think there must be a reason why someone has chosen to put a 20a on what seems to be a ring.
The 20a type C suggestion is good, assuming you can get an EFLI result low enough.
Working on the principle that the information the OP has given us is correct then a 32a would be a good solution.
They said that it is a ring and the 20a was installed at the time as that was what they had to hand.
If the installation paperwork verifies this then I see no issue.
My personal advice would be to get a local sparky to do the swap so they can carry out required tests etc. and ensure the correct part is installed.
Obviously there is no such thing as a 10 minute job :D but this is pretty close. :)
 
Working on the principle that the information the OP has given us is correct then a 32a would be a good solution.
They said that it is a ring and the 20a was installed at the time as that was what they had to hand.
If the installation paperwork verifies this then I see no issue.
My personal advice would be to get a local sparky to do the swap so they can carry out required tests etc. and ensure the correct part is installed.
Obviously there is no such thing as a 10 minute job :D but this is pretty close. :)
OP replied before I posted mine. >.<
 
Best EV Chargers by Electrical2Go! The official electric vehicle charger supplier.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

Joined
Location
Essex
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)

Thread Information

Title
Table Saw trips RCBO
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
18
Unsolved
--

Advert

Thread statistics

Created
Bedders,
Last reply from
HappyHippyDad,
Replies
18
Views
2,090

Advert

Back
Top