Gavsparky

Hi all,

Just a query I have, I'm working on new build houses and the meter intake is some distance (say 15-20mts) from the consumer unit, would I be right in using SWA 25mm 3 core to supply the CU. Also which termination method would one use at the external intake position as space would be limited for an adaptable box. I don't like glanding the SWA at the CU and leaving it inside as many do. Cheers for your thoughts.
 
Is the meter outside?

You don't NEED to use SWA, unless it is going to be concealed in a wall (or run outside?). Remember, if the tails pass through an internal wall, this doesn't need to be SWA either. It will need fusing down (if an 80amp fuse in main cutout then use a 60amp) as well.
 
its the length of run...

you will most likely need a KMF as kingeri has suggested....

check the rating of the bullit....then select fusing in KMF to suit....
 
Is the meter outside?

You don't NEED to use SWA, unless it is going to be concealed in a wall (or run outside?). Remember, if the tails pass through an internal wall, this doesn't need to be SWA either. It will need fusing down (if an 80amp fuse in main cutout then use a 60amp) as well.

Why the derating from the cutout.... kind of limits the available KVA to the property just because you have fitted a switch/fuse.

Note! DNO fuses are usually type (iii or iv) and will give partial at best discrimination through S/C to a type (ii) fitted in your switch fuse.
Disrimination to overloads is usually not an issue as the design of the installation shouldn't permit excessive loading and you could in fact comfortably match the DNO fuse or derate down from it without concern.
 
Last edited by a moderator:
I did this recently I used a 6inch wiska box and placed a henley block inside to join to normal meter tails at the meter end I placed a 100amp isolator and fuse, ukpn came and reconnected new supply. I used 3core I think if I was to do it again I would consider using 2 core and either using the sheath or running a separate earth as the 3 core wasn't very flexible and was hard to run.
 
I've always tried to obtain some degree of discrimination, perhaps it is a waste of time.
 
I've always tried to obtain some degree of discrimination, perhaps it is a waste of time.

When we discuss discrimination it is usually associated with fault current and thus the DNO will delay against a similar fuse of lower type giving in the OP example partial discrimination ... you may have full discrimination upto say 300amps fault current but as most supplies will have a S/C current in excess of 1000amps then only partial is achieved and no guaranteed order of operation can be achieved.

Ill edit my comment it reads slightly misleading ... where you wish to achieve order of operation of protective devices through overload and not fault then you can maintain the same size rating as the DNO if your device has a time curve that will operate your device quicker if you use same type of devices then this won't be achieved as the time curves for small overloads are identical between types ii, iii and iv.

If you are in a standard domestic setting with gas heating then you can relax a little here and fit your 60amp against 80 DNO as its unlikely to ever be reached.
 
The run of cable can be used internally in the house via joists and partition walls, but I'm thinking as SWA isn't the best working practise due to structure of cable, is there another option I can use which is easier to work with and terminate?
 
The run of cable can be used internally in the house via joists and partition walls, but I'm thinking as SWA isn't the best working practise due to structure of cable, is there another option I can use which is easier to work with and terminate?
if your going to run tails within partition walls then you need to provide additional protection for them....
 
Ie. RCD at intake? But is there a common used cable that can be used for this type of run (15-20mts) other than SWA?
 
I must add the meter is outside in the usual external domestic box enclosure, as you all know very limited to space for extra components.
 
Ie. RCD at intake? But is there a common used cable that can be used for this type of run (15-20mts) other than SWA?
if you are going to be running this feed in partition walls etc then an SWA would be the cable of choice....

then its just a case of RCDs for the finals...
 
What I'm trying to ask mate is an alternative to SWA as it's not the best to work with or terminate in these circumstances.
 