why the hell are you faffing about with adaptable boxes and these switches ? ?!?!?

might as well just get the Wylex 110m range of switches ! easy to terminate 25mm SWA and the like.

WY110M.JPG
no messing about !!!

dont you need to fuse these SWA submains anyway ? or are they all ready suitably fused upstream ?
 
Last edited by a moderator:
why the hell are you faffing about with adaptable boxes and these switches ? ?!?!?

might as well just get the Wylex 110m range of switches ! easy to terminate 25mm SWA and the like.

View attachment 17500
no messing about !!!

dont you need to fuse these SWA submains anyway ? or are they all ready suitably fused upstream ?

Nice soloution, but 12 No. Wylex 110M = about £800
If it was only for one or two, I would go for this.
 
As has been mentioned, if the CU is more than 3m away, it's almost certain that the DNO will require additional fusing.
i would go with individual fuses per CU, and mount the whole lot on steel trunking. It's cheap, easy to use and won't take long.
Make sure the locknuts are tight. I would fly lead from the trunking to each individual switch fuse.
will the armour on the 16mm 2 core be upto the spec for the bonding if its TNC-S? suspect not, but I'm not aware of all the facts as you are.
Don't forget that for main bonding of PME supplies, it's the conductivity that is of prime concern, unlike the adiabatic, in which limiting temperature is the concern.
 
As has been mentioned, if the CU is more than 3m away, it's almost certain that the DNO will require additional fusing.
i would go with individual fuses per CU, and mount the whole lot on steel trunking. It's cheap, easy to use and won't take long.
Make sure the locknuts are tight. I would fly lead from the trunking to each individual switch fuse.
will the armour on the 16mm 2 core be upto the spec for the bonding if its TNC-S? suspect not, but I'm not aware of all the facts as you are.
Don't forget that for main bonding of PME supplies, it's the conductivity that is of prime concern, unlike the adiabatic, in which limiting temperature is the concern.

Well spotted, yes all the CU's are more than 3M away. I was just driving back and thought I should mention this, but you beat me to it. This is one reason for using the Wylex Rec Isolators. I assume they are okay for the job?

Also worth mentioning is I also chose these for size as we don't have a lot of room in the intake cupbord.
 
Last edited:
Well spotted, yes all the CU's are more than 3M away. I was just driving back and thought I should mention this, but you beat me to it. This is one reason for using the Wylex Rec Isolators. I assume they are okay for the job?

Also worth mentioning is I also chose these for size as we don't have a lot of room in the intake cupbord.

The Wylex REC isolators aren't fused; so not OK.
 
If you have 12 number of flat's to supply, you maybe better off thinking about a Ryefield panel at the intake cupboard Where all the fuses are located in the one panel.

What do you have there, a 3 phase DNO supply??
 