if it was me, i would use an individual box for each and use the piranha nuts for each gland to give yourself the best chance of keeping you Zs down

Thanks for advice on piranha nuts, sounds like a good idea, but I don't understand the comment on individual boxes, can you elaberate?

Thanks
 
Electric Intake 3.jpg
Slight revision, Cut-Out is slightly bigger, I've also set meters directly on trunking to reduce overall height and lift lower switchfuses.

UKPower Networks and EDF have both approved design, but I would be greatful of any further suggestions.

Thanks
 

Attachments

  • Electric Intake 3.jpg
    Electric Intake 3.jpg
    720 bytes · Views: 90
Last edited:
Looks good and well thought out, however supporting and terminating the SWA's into the 110M's is going to be tight

Also have you confirmed that a 10m clearance on the bottom of the Ryefield is ok with the DNO
 
It's a big job, electrician is doing the work. This is just a small part of the job. The SWA runs off in a straight line, so no problem with SWA.
Well spotted, the cupboard is 90mm short, but I can easily make it higher, it's width that I can't do anything about.
I'll be making adjustment to cupboard, putting mounting board in and mounting Wylex on the wall, then DNO fitting Cut-Out, EDF fitting new meters and sparky connecting back to CU's.
UK Power Networks have agreed Cut-Out 100mm from floor is okay.
 
Last edited: