Hi all,
I've installed a Tesla Gen 3 wall charger supplied by my client.
For your information, the place that I installed is in a block of flat basement where the Meter room is.
After some researching, I've fitted a Proteus board fitted with SPD and PEN fault detection device.
All dead test result is fine. Ze and PFC at the board is fine as well.
Testing with the ev tester, everything goes fine until RCD testing with the tethered socket.
I've set the pp state at 32amp and CP state knob at C, once the mft goes to RCD testing stage, it shows a reading for the dc mA and the charger flashing red light and no power at the tethered lead. The strange thing is the RCD at the board didn't trip.
I've noticed at the app it said that the Ground Fault interrupter is enable, will this affecting the RCD?
I want to know is there any thing that I've done wrong or missed?
Thanks for all the help.
 

Attachments

  • IMG-20230809-WA0018.jpg
    149.7 KB · Views: 17
  • IMG-20230809-WA0019.jpg
    193.4 KB · Views: 16
  • IMG-20230809-WA0017.jpg
    208.2 KB · Views: 18
  • 20230809_180655.jpg
    475.2 KB · Views: 15
How are you connecting the mft to the tethered socket? Could you do an rcd ramp test at the ccu whilst having the tethered socket plugged into car or even a dummy resitive load?

Reason I say this is the charger likely has some logic and inductive current sense which even tho is getting CP and Pp may not be outputting any current to and open socket, We test the EV chargers at my firm with resistive load banks.

Maybe someone more experienced with tesla chargers will offer some insight..
 

Reply to Tesla Gen 3 wall charger commissioning in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Afternoon everyone, I have a quick question about the Tesla Gen 3 Wall Charger? Does it require Type A 30MA RCD protection or not. Only because...
Replies
3
Views
1K
Morning all, I'm wondering if anyone has much experience with the Tesla Gen 3 Wall Chargers? Quick look through the instructions shows no PEN...
Replies
2
Views
778
Hi. Not sure if it's the right place to ask, so won't be upset if it gets removed. Apologies if the terminology (PEN/PME/etc) is used...
Replies
44
Views
7K
Has anyone installed the Gen 3 Tesla EV charger. Is an RCD required at the supply as it says it has a type A one built into the unit. Also can...
Replies
4
Views
3K
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock