Apologies if I am missing the blindingly obvious here but why do you need to disconnect the main bonds to do the tests?

Are we not looking for exposed metalwork which requires bonding after main bonding has been applied? There is surely a possibilty that you will find a bunch of exposed pipes which are continuous metal from the incoming supply that will be identified by this test as needing supplementary bonding despite the fact that these pipes will be effectively bonded when the main bonding is re-connected. You coukd end up adding extra bonding unecessarily.

What is supplementary bonding actually supplementary to? I was under the impression that it is a bond intended to supplement the main bonds? ie: a bond which is applied after the main bonding to supplement it where needed.
 
OP, you are testing whether the pipe is extraneous (i.e. already effectively already at Earth(ish) potential)...with that in mind you leave the Earth connected at the MET when testing with an Insulation Resistance tester - you are comparing "the lump of metal in question" with a known Earth potential.

You don't have to leave it connected to the MET. In fact, I usually find it easier to disconnect the main earth cable from the MET, rather than taking everything else out.
 
I am not sure if the original question relates to main or supplementary bonding and I think some posts are referring to one and some to the other.

Apologies if I am missing the blindingly obvious here but why do you need to disconnect the main bonds to do the tests?

For main bonding - to determine if a part is extraneous in itself, obviously any connections it may have to the met and other extraneous parts should be removed.

For supplementary - all main bonding and cpcs will be left connected.



Are we not looking for exposed metalwork which requires bonding after main bonding has been applied? There is surely a possibilty that you will find a bunch of exposed pipes which are continuous metal from the incoming supply that will be identified by this test as needing supplementary bonding despite the fact that these pipes will be effectively bonded when the main bonding is re-connected. You coukd end up adding extra bonding unecessarily.

What is supplementary bonding actually supplementary to? I was under the impression that it is a bond intended to supplement the main bonds? ie: a bond which is applied after the main bonding to supplement it where needed.
Yes.
 
So basically if I had paid more attention and actually read the thread properly my question would not have been necessary!
 