paddyscouse

can some one explain in detail, laymans terms please, how to do an rcd test on a rcbo board at the board (im not talking about socket circuits)
i have an assesment soon and want to get this part right, will it be ok to rcd test at the board or should i do at the lighting point ?
if im to test at board do i connect to terminals on rcbo or do i connect to nuteral flex on rcbo, do i conecct to earth flex on rcbo or earth bar, or as ive been told do i connect tails in to terminals to avoid no trip issues due to direct contact. can some one help me on this ?
 
The only time a consumer unit cover should be removed is when the main switch is off,so testing an RCD/RCBO at the consumer unit would be hard as to test it you need it to have the supply on.
Test at a point along the circuit as close to the consumer unit as you can,testing the sockets can be done with the plug lead supplied with your test kit,testing the rcd/rcbo on a lighting cct can be time consuming as you will be re setting the rcd/rcbo a number of times,hence carrying out the test as close to the consumer unit as you can.
 
can some one explain in detail, laymans terms please, how to do an rcd test on a rcbo board at the board (im not talking about socket circuits)
i have an assesment soon and want to get this part right, will it be ok to rcd test at the board or should i do at the lighting point ?
if im to test at board do i connect to terminals on rcbo or do i connect to nuteral flex on rcbo, do i conecct to earth flex on rcbo or earth bar, or as ive been told do i connect tails in to terminals to avoid no trip issues due to direct contact. can some one help me on this ?

It depends on the make of the RCD / RCBO. Some you can test directly from terminals others you need to install a short length of cable to the terminals and test from that. The neutral flex is connected to the neutral bar so not much point in testing from there as it is upstream of the device.
 
The only time a consumer unit cover should be removed is when the main switch is off,so testing an RCD/RCBO at the consumer unit would be hard as to test it you need it to have the supply on.
Test at a point along the circuit as close to the consumer unit as you can,testing the sockets can be done with the plug lead supplied with your test kit,testing the rcd/rcbo on a lighting cct can be time consuming as you will be re setting the rcd/rcbo a number of times,hence carrying out the test as close to the consumer unit as you can.

An RCD / RCBO should be tested at the device with the loads disconnected. Live testing can not be avoided and is perfectly safe if carried out with the correct equipment in the correct manner.
 
The only time a consumer unit cover should be removed is when the main switch is off,so testing an RCD/RCBO at the consumer unit would be hard as to test it you need it to have the supply on.
Test at a point along the circuit as close to the consumer unit as you can,testing the sockets can be done with the plug lead supplied with your test kit,testing the rcd/rcbo on a lighting cct can be time consuming as you will be re setting the rcd/rcbo a number of times,hence carrying out the test as close to the consumer unit as you can.

ok thanks, so you advise to test at closest point on cct especialy if its my assesment! just to confirm i conecct to l n e or can it be just l+n
 
Test at the board, put a croc clip in the earth bar and test from one of the connected MCBs
 
On an assement ? id fail you without you getting your `croc clips out`

What a load of tosh. What is so wrong with a competent person carrying out a live test inside a cu. I have an assessment every year and not once have I been failed for testing correctly and inline with the manufacturers recommendations.
 
Testing an RCD/RCBO is always a 3 lead test. If your carrying out your assessment on a mock install you may have a pendant and flex, unscrew the rose and just test with relevent leads on line,neutral and earth and start your test,rememeber it may be fiddly but DO NOT remove those covers on the tips of your test leads or your assessor may be reaching for GS38.
 
why ? please elaborate

Why?
sorry paddy, I was asking why would slinky fail me, I can't see anything wrong with the way I was do it. He didn't give any reasons, just a random comment, then nothing to back it up.
from my point of view, as long as any live parts in the cu are protected its a safe place to work. You have plenty of space to work.
 