Not saying it's the case on all ups systems/units, but I've tested one unit that had a zs of 0.14 ohms into the unit, and anything past the ups had a reading of at least 1.49 ohms, so our readings weren't poor, the ups was almost ramping up the resistance on the earth path on live tests, but all dead tests ie R1+R2 were fine, hope this helps