Not saying it's the case on all ups systems/units, but I've tested one unit that had a zs of 0.14 ohms into the unit, and anything past the ups had a reading of at least 1.49 ohms, so our readings weren't poor, the ups was almost ramping up the resistance on the earth path on live tests, but all dead tests ie R1+R2 were fine, hope this helps
 
Not from my experiences, I've tested 2 ups systems, both were 'riello' units. Its just like normal testing, I did however disconnect the feed from the ups fed db to do my insulation resistance tests, just in case it sent a nasty surprise upstream to the ups unit!
 
Well I for one am very confused. Ups sockets? surely you speak to the client, unplug the ups and treat as normal socket outlets, if it is connected to fused spur units then disconnect flexies and then test, unless I have missed something then I apologise.
 
Haven't full checked it out , just having natter about it. Yes with you.

I know the ups board is fed by 25mm as is about 100m from ups unit.

i installed a smaller 1 which takes a fused feed, then leads come out to fused spurs then off to locations of ups sockets.

so i know not to IR test it just wasn't sure about doing zs test through ups unit. On high or no trip , would it make a difference
 
You should not carry out Zs testing on UPS backed circuits, UPS's have high earth leakage and will give incorrect results.
If there is an External bypass switch then operate this so that it's not running through the UPS. If there isn't an external bypass Sw then you need to turn the inverter off on the UPS so that the UPS itself is in Internal bypass.
Obviously check with the customer this is ok to switch if already supporting critical load just in case you drop the load!!!
 
I did two circuits on low last night and readings did seem slightly high but still under max zs
 